In regard to the furnace thread, I recently had to remove the phantom load
effect of a multiple-zone hydronic boiler. Each zone has a dedicated Taco
circulator instead of a zone valve. The pumps are energized through a Taco
control box, based on the 24vac t-stat closure for each respective zone. We
used double pole, single throw line voltage thermostats. The main boiler /
control 120vac power is paralleled through pole 1 of each thermostat. Pole 2
of each t-stat is wired into the Taco control box. Whenever there a T-stat
calls for heat, the boiler and controls are powered up by 120 vac, and the
the 24 vac closure is made, instructing the individual circulator to turn
on.
t-stat part# is Mcmaster-Carr 17395K95
Vermont Solar Engineering - a Xantrex / Trace Certified Dealer
Kirk Herander
PO Box 697
Burlington, VT. 05402
www.vermontsolar.com
www.backeastsolar.com
800.286.1252 - 802.863.1202
fax 802.863.7908
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-Wrenches
mailing list