I notice how quick the Canon/Unisolar range has been discounted for use with the
PV series inverters.
I have done several array designs with these products.
The EF2-64 'Econoflat' roof module will perform well with this inverter.
The VOC max. at Zero degrees Celsius is under 600 Volts with a 27 module string.
The MPPT remains within the window of 300-480 right up to a 70 degrees celsius
module temperature.
Please do not discount these products without being sure of their behavior.
Please also note that the US64 has a much different MPPT curve and the
Canon/Unisolar range cannot be assumed to fall into one spec.
Carl Emerson
Manager
FREEPOWER LTD. "Harnessing Natural Energy" Auckland, NEW ZEALAND.
- - -