PV Inverters module strings [RE-wrenches]
Eric Smiley
Eric_Smiley at bcit.ca
Wed Mar 28 18:46:42 EST 2001
Thanks to Bill and Kent.
If I understand this correctly:
a) The upper limit of 600 V max Voc is fixed by the NEC/CEC.
b) The lower limit is fixed by the line voltage.
c) There isn't a thing we can do about this.
We just need PV modules with a good Fill Factor so that they don't
wander below the MPPT window during high temperatures, and don't exceed
600 V at low temperatures.
----------------------------------------------------------------------
Eric Smiley
Project Leader - BCIT Technology Centre
Photovoltaic Energy Applied Research Lab (PEARL) - BCIT
ph: (604)432-8657 www.bcit.ca/~tc/pearl/index.htm
- - - - - - -