Power Centers, multiple inverters [RE-wrenches]
Roy Butler, Four Winds RE
roy at four-winds-energy.com
Thu Feb 15 09:13:04 EST 2001
Hi Allan,
I agree with what the others said about the stacked SW inverters. And
add this....I've had 2 stacked SW4024s and 2 stacked SW5548s working since
'99 with no problems...all with grid backup/ battery charging.
Warning....some of the settings are trickier to tweak due to the dual
nature of the system, but otherwise not a problem. You CAN use both
chargers....I have them turned down to the point where the 2 share the
work, instead of putting all the stress on 1.
I followed Trace's suggestion of offsetting the bulk charge voltages by
.2 volts and it worked fine....one inverter shuts down first and the 2nd
follows shortly thereafter. This eliminates cycling between the 2.
As for running 3 inverters....I've had one of those systems up and
running since the summer of '99. Works good....we jumped thru the hoops to
zone (re-wire) the existing house, but since you're doing this in new
construction, piece of cake! We put a 2nd battery bank in for the 3rd
inverter while we were at it (mostly because the 3rd inverter was an add-on
to an existing system). And we connected lighting, ceiling fans, seldom
used outlets and other non-critical loads to the 3rd inverter....so far, so
good.
Bottom line...go for it! I totally agree with your philosophy of
keeping it simple.....and understand your reservations regarding a complex
system like this, but it really does work!
FYI...we didn't use a power center, although in retrospect, that
probably would have been a lot easier to wire!
Roy Butler
Four Winds
Arkport, NY
www.four-winds-energy.com
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-Wrenches
mailing list