Marco,
We have done quite a few stacked pairs, so we have seen the problems you
mention, especially the one about both shutting down if one goes down. I
was asking specifically about Trace's newer parallel interface, to allow 8
or 11 kW at 120VAC. I don't really expect to use it, for the reasons I gave
in the original posting, but I want to be able to better defend my system
design.
>Re:If any battery charging is going on, I believe that Trace recommends
using one inverter only to battery charge.
No, both can charge, you just set the absorption times a bit off.
Thanks for your contribution.
Allan at Positive E
I've had a dual SW5548 systems with stacking interfaces in the field since
late 1999. All is working well as far as I know. One important thing to
know: if one inverter is having a problem of any kind, they both will go
down. If any battery charging is going on, I believe that Trace recommends
using one inverter only to battery charge.
marco
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-Wrenches
mailing list