<x-flowed>Hello Jack

I think more like bad power factor in the Trace's charger. We measure 
between 0.73 and 0.76 here for the power factor on a Trace SW4024 
powered by a Honda ES6500.

Richard

At 01:25 -0800 12/20/00, Jack West, Talkeetna AE wrote:
>Hi Steve,
>
>I have seen this exact thing with a 3500 watt Honda and 4024.  Had to drop Gen
>Size down to about 25 amps and Max charge rate to 18 amps for system to work
>properly.  Clamp on amp meter showed 29 amps delivered from genny at 
>full load.
>Inaccuracy of Trace metering? I guess so.
>
>Steve Willey, Backwoods Solar wrote:
>
>  >   Also a
>  > clamp on external meter will show more amps actually entering than the
>  > setting or the Trace meter.  Customers have reported this several 
>times, and
>  > I have owned two generators where this discrepancy is observed.  Any one
>  > have like experiences or explanation?
>  > Steve Willey   www.backwoodssolar.com
>  > Backwoods Solar Electric Systems
>  >
>  > - - - - - - -
>  > To send a message:
>  >  RE-wrenches at topica.com
>  >
>  > The archive of previous messages:
>  >  http://www.topica.com/lists/RE-wrenches/
>  >
>  > To unsubscribe send a message to:
>  >  RE-wrenches-unsubscribe at topica.com
>  >
>  > To check out the other RE-Wrench participants:
>  >  www.mrsharkey.com/wrenches/index.html
>  >
>  > Hosted by Home Power magazine:
>  >  www.homepower.com
>  >
>  > For info contact list moderator by email:
>  >  michael.welch at homepower.com
>  >
>  > ___________________________________________________________
>  > T O P I C A  http://www.topica.com/t/17
>  > Newsletters, Tips and Discussions on Your Favorite Topics
>
>- - - - - - -
>To send a message:
>  RE-wrenches at topica.com
>
>The archive of previous messages:
>  http://www.topica.com/lists/RE-wrenches/
>
>To unsubscribe send a message to:
>  RE-wrenches-unsubscribe at topica.com
>
>To check out the other RE-Wrench participants:
>  www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine:
>  www.homepower.com
>
>For info contact list moderator by email:
>  michael.welch at homepower.com
>
>___________________________________________________________
>T O P I C A  http://www.topica.com/t/17
>Newsletters, Tips and Discussions on Your Favorite Topics

------------------------------------
Richard Perez
Home Power
PO Box 520, Ashland, OR 97520  USA
Tele: 530-475-3179
FAX: 530-475-0836
Subscriptions: 800-707-6585
mailto:richard.perez at homepower.com
Web: http://www.homepower.com

- - - - - - -
To send a message:
 RE-wrenches at topica.com

The archive of previous messages: 
 http://www.topica.com/lists/RE-wrenches/

To unsubscribe send a message to: 
 RE-wrenches-unsubscribe at topica.com

To check out the other RE-Wrench participants:
 www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine: 
 www.homepower.com

For info contact list moderator by email:
 michael.welch at homepower.com

___________________________________________________________
T O P I C A  http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics

</x-flowed>


More information about the RE-Wrenches mailing list