Inverter protection [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Mon Dec 4 11:49:24 EST 2000
<x-flowed>Doug,
I don't sell or install Power Panels and THAT is one of the reasons.
As I recall, the wire that they provide to go from the inverter side
of that 250A CB to the RE inputs is 6AWG as well. The one Wes Edwards
and I installed as volunteers for a non profit had that #6 going
right up into the battery positive input of a C40 controller. Meaning
that should you have a fault in the controller, that #6 was protected
only by a 250A CB. Lovely, and it apparently is OK with UL which
tells me something about the whole testing lab deal. As to protecting
the inverter DC inputs from gross overvoltage, I THINK the C40 (or
whatever) should block PV voltage if powered down. The wind genny is
another matter entirely. Usuall, I remove the skinny #10 wire from
the battery side of the big Henie and replace it with something more
substantial BEFORE I assemble the DC 250. Of course, with your PP
that defeats the whole purpose of buying a prewired, UL approved
unit. Your only options I think, would be to shove a wire up with the
4/0 on the hot side of the big CB, feed it to a smaller downstream CB
or safety switch and on to your Whisper load center (or whatever).
OR, feed the Whisper load center (thru a DC rated CB or RK-5 fused
safety switch) directly from the battery. A bit uglier, but at least
safe.
Good Luck, Bob-O
>I have a question for the expertise of this group. We are in the final
>throws of completing a system (2 racks of 4 ASE 300W modules on trackers and
>3000W Whisper (I think), 2 Trace 5548s for 240V on a Trace Power Board,
>about 2000 Ahr battery bank, 20Kw generator, purchased as a package from
>Kiocera ("It will take an electrician only a few hours to get it up and
>running!")). The power inputs (PV and wind) are connected to the inverter
>side of the 250A battery disconnects, which is our question. It seems to
>leave the inverter unprotected - you're able to isolate the batteries, but
>to isolate the inverter you need to turn off the PV and wind input
>separately. This would seem to make sense, but it seems that an inattentive
>or inadequately trained homeowner might easily turn off the battery main,
>thinking they were disconnecting power to the inverter, when in fact the PV
>and wind would still be powering the units. We actually did this (left only
>the wind connected), and one of the inverters smoked. So, I would
>appreciate any thoughts and/or remedies.
>Doug McCorkle
>Sunnyside Solar
Bob-O Schultze, Electron Connection
PO Box 203, Hornbrook, CA 96044
800.945.7587 fax 530-475-3401
www.electronconnection.com
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics
</x-flowed>
More information about the RE-Wrenches
mailing list