<x-flowed>>
> So....If I'm seeing Ah consumption being replaced at 99% of
>the charging
>current (as calculated by the E-meter, and by direct observation), what is
>the actual battery efficiency? Sounds to me like 99% of what goes in as a
>charge comes out and is delivered to the load.
If 99% of AH in is going out to the load (sounds very dubious) then
far less WATT-hours are going out, and that is the true battery
efficiency -- because the voltage is higher during charging than
during discharge. Simple!
So, to make a complete statement about efficiency of batteries, you
need to distinguish between AH efficiency and WH efficiency.