I may be answering my own question here, someone tell me if I'm right:
Overall battery efficiency must take into account not only Ah of
consumption, but terminal voltage during charge/discharge to provide Kwh
readings which can be compared.
Example:
In my EV, (using greatly rounded-off values), 45 Ah of consumption at a
terminal voltage of 100 VDC = 4.5 Kwh. Recharging the batteries puts back
approx 46 Ah at ***125 VDC*** = 5.75 Kwh. 4.5 / 5.75 = .78 or 78%
efficiency. This is a lot closer to the 80% figure that I have always
understood was correct for L/A batteries.
Obviously, to get an accurate calculation, one would have to log the
actual terminal voltage over the entire charge/discharge period, no easy
task, especially in an EV, where the terminal voltage ranges from 90 - 130
volts over that period. Sounds like a job for a micro-controller and analog
input device.
Too high tech for me, I gotta go rake leaves....
-S
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list