SW2512 and pump problems [RE-wrenches]
Don Loweburg, Offline
i2p at aol.com
Wed Sep 13 12:24:35 EDT 2000
In a message dated 09/12/2000 11:21:51 PM Pacific Daylight Time,
jackwest at alaska.net writes:
<< Wrenches,
I have a customer with a SW2512, 1400AH battery. Every time pump comes on,
system browns out enough to cause computer and TV problems (crashes and
resets). Pump is 1/3 HP 115 VAC two wire sub pump, approximately one year
old. Pump runs OK. Well is not deep, maybe 40 feet. Even browns out with
open discharge from pump. Any suggestions? This is the first two wire pump
I
have seen on a SW inverter. Is this the problem? Any suggestions would be
appreciated.
>>
DC side seems pretty ok. What about on the as distribution side, wire size,
connections etc.
You might also check both the DC start amps and the Ac start amps to see
what might be going on.