Bob-O suggested...
>Try setting the Gen Amps AC (Menu #11) higher than the Max Charge
>Amps AC (Menu#10). Say, 40 and 30. You should be able to get close to a C-
>10 charge rate to your 1270 A/hr battery with the 30A default Max Charge
>Amps, or even a little less. Unless....the peak to peak ac voltage of
>that Kohler is low. Grid is 164, most gennys run somewhat lower, but
>you need to have 155 or better under load to make the charger
>perform. Don't know if you have other loads, but bear in mind that
>the 4024 in charger mode is only about 55-60% efficient.
I've always made those two settings the same, usually 30 Amps, assuming
the genny could handle it (two Honda 6,500 Watt machines can only deliver
19 Amps without being dragged down, despite the Honda outlet being
labeled 120 VAC, 27 Amps).
This Kohler 12RY was re-wired for 120 VAC only and is fueled by LPG
(propane). With altitude de-rating, it delivers about 10.8 kW. I'll use a
Fluke 87 to measure the Kohler Peak RMS on my next visit. Many Hondas
show about 170 V. Peak, whereas my 30 kW Onan only delivers 157 V. Peak.
There were no other loads while the Kohler ran for 6 hours yesterday.
Cordially, Chuck
SUN-tricity®
Big Oak Flat CA - where "our local park" is called Yosemite
- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>
To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/
To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>
To check out who the other RE-Wrench participants are, go to <http://www.mrsharkey.com/wrenches/>
Hosted by Home Power magazine: <http://www.homepower.com>
for info contact: <michael.welch at homepower.com>
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list