On the domestic SW's, the inverter disconnects from the genset if the voltage rises above a
programmable set point (default 132 VAC). I've seen this happen on several occasions when large
loads were turned on. The loaded leg would drop in voltage and the other leg would rise in voltage,
keeping the leg to leg voltage constant. These problems stem from voltage regulation issues on the
generator, not the inverter.