RE TEST LAB - EXPERIMENT 1 [RE-wrenches]
Bob-O Schultze
econnect at snowcrest.net
Fri Feb 25 15:49:24 EST 2000
<x-flowed>>Dear Drake and Don,
Good Show!
I generally use a GOOD QUALITY welding cable for all my
installations. It's Essex Excelene, rated from +105C to -50C 600V,
but not UL. I use a heavy duty crimp lug and glue filled heat shrink
to seal it. I've never had a problem or failure of any kind. I do
have some UL listed 427 strand stuff marked RHH/RHW/USE 600V in 2/0
and 4/0 on hand in case I HAVE to use it, but it's about $1.50 more
per ft (4/0) and I just can see how the performance difference could
possibly be different. We're running what, 60VDC MAX thru the stuff?
That's a 10X safety factor and the stuff is DESIGNED to spend its
whole life living in a sparks shower and being dragged across cement
floors in welding shops. For crying out loud...
Finely stranded wire is absolutely a necessity for inverter cables.
You might get by with THHN for battery interconnects, but why fight
with it?
I came behind a system once where the installer ran 4/0 THHN from the
battery, thru a 6x6 chase, up into the Trace disconnect, and into the
breaker. Unfortunately, I had to disassemble this mess. Thought I'd
break an arm getting it out of there. No THHN for me, thanks.
Keep up the super work.
Bob-O
>QUESTIONS FOR WRENCHES
>
> So far, the only parameter that we have been able to come up
>with that is unique for battery compartments is acid resistance. Do
>any Wrenches know of other parameters that may be important?
>
> Traditionally, battery and inverter cables have been of the
>finely stranded variety. (2/0 Hypalon Diesel Locomotive cable has
>427 strands). In the past, before inspectors wanted to be involved
>with RE systems, I (Drake) had used 2/0 THHN in certain
>installations, which has 19 strands (according to NEC Table 8).
>This cable seemed to work fine. Where it needed bending, I would
>pre bend it to avoid stress on terminals. I have never tried to put
>THHN inside of a Trace disconnect enclosure, but imagine that it
>would be difficult. Does anyone feel that using finely stranded
>cable is (or is not) necessary?
>
> What other types of cable should we be testing?
>
> Any information about success or problems with the use of
>various cable for battery interconnect would be appreciated.
>Especially important, has anyone had problems with using welding
>cable in association with battery banks? Does anyone have evidence
>indicating that welding cable is adequate?
>
>THE LAB'S MISSION
>
> This lab is dedicated to determining what is technically
>necessary for safe renewable energy systems. Our hope is to find
>ways to eliminate unnecessary expenditures, to allow for more people
>to be able to afford these systems.
>
>
> Sincerely,
>
>
>
>Drake Chamberlin
>
> Electri
>cal Energy
> (303) 399-1025
>
> Don
>Wallingford
>
>Quicksilver Electrical Service
> (303) 833-4214
Bob-O Schultze, Electron Connection
PO Box 203, Hornbrook, CA 96044
800.945.7587 fax 530-475-3401
www.electronconnection.com
- - - - - - -
To send a message to the list use: <RE-wrenches at topica.com>
To view an archive of previous messages go to: <http://www.topica.com/lists/RE-wrenches/
To unsubscribe send an email message to: <RE-wrenches-unsubscribe at topica.com>
Hosted by Home Power magazine: <http://www.homepower.com>
for info contact: <michael.welch at homepower.com>
_____________________________________________________________
Want to find the best email lists? Check out the Topica 20!
http://www.topica.com/topica20
</x-flowed>
More information about the RE-Wrenches
mailing list