<x-flowed>>Series connecting shunts is also not necessary to connect multiple meters
>of the same sensitivity. My system has two 50mv meters connected across one
>shunt, with no discernable change in accuracy. The meter movement's
>internal resistance is insignificantly high in comparison with the very low
>resistance of the shunt, so no functional change in the shunt's resistance
>is induced by the second (or third, fourth, etc) meter.

- S

I ditto on the above, and it's good to know. For instance when 
installing a shunt metering system and a Solar Boost controller, the 
S Boost has an option to hook it to an external master shunt for 
smarter regulating. Connect it to the same shunt as the meter, then 
set the S Boost to the shunt characteristics. Very easy to do. 
Confirmed OK in numerous installations.

Happy Solstice


Oh, and Smitty -- Congratulations. You've passed the initiation.

Windy

- - - - - - -