SW inverter and generator cycling in and out [RE-wrenches]
Jack West, Talkeetna AE
jackwest at alaska.net
Wed Dec 20 04:25:20 EST 2000
Hi Steve,
I have seen this exact thing with a 3500 watt Honda and 4024. Had to drop Gen
Size down to about 25 amps and Max charge rate to 18 amps for system to work
properly. Clamp on amp meter showed 29 amps delivered from genny at full load.
Inaccuracy of Trace metering? I guess so.
Steve Willey, Backwoods Solar wrote:
> Also a
> clamp on external meter will show more amps actually entering than the
> setting or the Trace meter. Customers have reported this several times, and
> I have owned two generators where this discrepancy is observed. Any one
> have like experiences or explanation?
> Steve Willey www.backwoodssolar.com
> Backwoods Solar Electric Systems
>
> - - - - - - -
> To send a message:
> RE-wrenches at topica.com
>
> The archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
>
> To unsubscribe send a message to:
> RE-wrenches-unsubscribe at topica.com
>
> To check out the other RE-Wrench participants:
> www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine:
> www.homepower.com
>
> For info contact list moderator by email:
> michael.welch at homepower.com
>
> ___________________________________________________________
> T O P I C A http://www.topica.com/t/17
> Newsletters, Tips and Discussions on Your Favorite Topics
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list