Trace/Kohler light flicker [RE-wrenches]
Joe Schwartz, Home Power
joe.schwartz at homepower.com
Tue Dec 12 21:21:41 EST 2000
<x-flowed>Travis,
>Joe,
>
>Go to menu 11 and check the the voltage input window. It might need to be
>widened to catch the voltage variances as loads come and go. Is this a
>Kohler powered 3600 RPM unit?
I don't have a clue where this inverter is installed but the inverter
isn't jumping off-line during charging. So the voltage input window
is probably OK.
>
>A Dual 5548 setup has over 7 kW worth of battery charging capability.
>Combine that with a few loads in the house and you are eating up all 8.5 kW
>of that Kohler. This is probably really pulling the voltage down, maybe just
>on one leg. Dual set ups have a habit of one inverter dropping into float
>as the other stays on bulk. It at that time where it all falls apart.
>Since the voltage is going to equal ~240 the generator will compensate by
>taking the unloaded (less loaded) leg's voltage up while the loaded leg
>voltage goes down. For example 135+105 still = 240 but outside of what the
>SW will accept in default settings. Check the Max AC 2 amps (assuming
>that's where the generator is fed into) and turn that down gradually to see
>if that solves the problem. The customer might even have to plug a large
>load (500+watts) on the unloaded leg to balance out the gennie. Don't
>laugh, "been there, done that".
>
>This can be easily verified if the "flickering" correspond with the "AC1 in
>Good" led going from solid to flashing. Watch the menu 4 input voltage as
>this happens also. I bet one is heading past 135 while the other drops to
>under 110.
>
>The Kohler tech's I've met are really sharp. If they bless the unit its
>probably OK. I have them commission our bigger (over 100 kW) units but
>rarely have them out on units under 20 kW.
Thanks for yer input Travis,
Joe
>
>Travis Creswell
>
>
>---------
>
> >Dear Joe:
> >
> >I am an avid reader of Homepower and read it cover to cover slowly.
> >Mr. Perez has been extremely helpful with a problem I have had with
> >an intertie problem I have had with my utility.
> >
> >I have a Trace Power Panel with 2-SW5548 inverters, 32-Trojan L-16
> >batteries, 24 Siemens 100 watt panels, and a Kohler 8.5 RMY genset.
> >
> > I am having a problem with the genset. It is set up for 120-240v
> >operation. The problem is when the genset is running the lighting
> >flickers from voltage fluctuation. Every type of light bulb does this
> >you can even see this if the TV is on. I have talked to Trace and
> >they say that when the genset is running it powers the AC loads and
> >operates as a battery charger.
> >
> >I recently had a Kohler authorized technician investigate the
> >problem. He set up the generator on a resistive load bank and the
> >generator worked fine. His diagnosis is that the inverters are
> >causing the genset voltage regulator to become unstable. He verified
> >that with me by showing me the voltage fluctate on an analog and
> >digital voltmeter.
> >
> >Have you ever had similar situations? Is there any possible
> >solution? I am very interested in your opinion and think very highly
> >of the staff at Homepower Magazine.
>
>- - - - - - -
>To send a message:
> RE-wrenches at topica.com
>
>The archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
>
>To unsubscribe send a message to:
> RE-wrenches-unsubscribe at topica.com
>
>To check out the other RE-Wrench participants:
> www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine:
> www.homepower.com
>
>For info contact list moderator by email:
> michael.welch at homepower.com
>
>___________________________________________________________
>T O P I C A http://www.topica.com/t/17
>Newsletters, Tips and Discussions on Your Favorite Topics
-------------
Joe Schwartz
Home Power Magazine
PO Box 520, Ashland, OR 97520 USA
email:joe.schwartz at homepower.com
Web: http://www.homepower.com
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A http://www.topica.com/t/17
Newsletters, Tips and Discussions on Your Favorite Topics
</x-flowed>
More information about the RE-Wrenches
mailing list