two Trace SW4048's in parallel [RE-wrenches]
Jeffrey Wolfe, Global Resources
global at sover.net
Sun Aug 20 00:51:07 EDT 2000
David, the only two things I can think of are:
1. The obvious - sign saying 120V, single phase only on the panel board
2. You may need separate, isolated neutral busses for each inverter in the
panel. May not. I've had some strange feedback into the Trace SW's from
common neutrals, and think this may cause a problem. (Something like the
inverter #2 thinking that it is getting its supply fed back into it's
input.)
Anyone else have an opinion on this?
Jeff
Jeffery D. Wolfe, P.E.
Global Resource Options, LLP
A Woman-Owned Vermont Limited Liability Partnership
4 Kibling Hill Road
P.O. Box 51
Strafford, VT 05072
802/765-4632
802/765-9983 (Fax)
global at sover.net
www.globalresourceoptions.com
----------
From: David Palumbo, Independent Power & Light[SMTP:ipl at sover.net]
Reply To: RE-wrenches at topica.com
Sent: Saturday, August 19, 2000 3:52 PM
To: RE-wrenches at topica. com
Subject: two Trace SW4048's in parallel [RE-wrenches]
Wrenches,
We are adding a second SW4048 onto a system for two reasons.
1) To increase the speed of battery charging (system has a large 120/240
Kohler genset).
2) To provide backup inverter power in case one of the SW4048's
should
fail.
This is a 120 volt system only so we will not be series stacking the two
SW4048's. The client
also does not need any more power on one circuit than one SW will supply.
Our idea is to keep the SW4048's independent of each other and simply wire
each inverters
output hot wire to a different leg in the AC load center. We have
successfully done this with
two Exeltech 1100's and I don't see why this should not work with SW4048's.
It is relatively
easy to balance the home's various circuits so that all of the big loads
will not be fed from
one inverter. For instance we will make sure that the water pump and
washing
machine are fed from
different inverters.
By doing it this way we will save our client the $ 345 for the Trace
SWI/PAR
paralleling kit.
Plus the extra labor to install, and the added system complexity.
We wanted to float this idea out to the list in case we are missing
something.
David Palumbo
IP&L
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-Wrenches
mailing list