25 A Isc is good. Thanks for pointing that out. I will consider using
the 12KW. I noticed that it accepts a lower voltage for the PV input,
but 2 strings can go on each MPPT.
On 2026-07-14 11:23, Jay via RE-wrenches wrote:
> Hi drake
>
> Unless you have high elevation or edge of cloud, you should be good to
> go.
> Max short circuit is 25 amps fyi.
>
> I've always recommended the 12kw. Only slightly more expensive but
> gives lots better out of balance load rating than the 6kw.
>
> Jay
>
>> On Jul 14, 2026, at 9:02 AM, Drake Chamberlin via RE-wrenches
>> <re-wrenches at lists.re-wrenches.org> wrote:
>
>> I am looking for a module to use with an EG4 6000 XP inverter. The
>> module I am looking at has an Isc of 14.47 A. Multiplied by 1.56,
>> that comes out to 22.6 A. The max current allowed on the PV input is
>> 17 A?
>>
>> A distributor thought it would be fine to use this combination. Do
>> you think it would be safe?
>>
>> Thank you,
>>
>> Drake