Jay jay.peltz at gmail.com
Tue Jul 14 08:23:36 PDT 2026


Hi drake

Unless you have high elevation or edge of cloud, you should be good to go. 
Max short circuit is 25 amps fyi. 

I’ve always recommended the 12kw. Only slightly more expensive but gives lots better out of balance load rating than the 6kw. 

Jay

> On Jul 14, 2026, at 9:02 AM, Drake Chamberlin via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> 
> 
> I am looking for a module to use with an EG4 6000 XP inverter. The module I am looking at has an Isc of 14.47 A. Multiplied by 1.56, that comes out to 22.6 A. The max current allowed on the PV input is 17 A?
>  
> A distributor thought it would be fine to use this combination. Do you think it would be safe?
>  
> Thank you,
>  
> Drake 
>  
> Drake Chamberlin
> 
> Athens Electric LLC
> 
> Ohio Electrical Contractor’s License 44810
> 
> NABCEP Certified PV Installation Professional
> 
>  
> --
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20260714/5995ff42/attachment.htm>


More information about the RE-wrenches mailing list