[RE-wrenches] kilovault 2400 HLX Lithium Battery Charging.....
Jay
jay.peltz at gmail.com
Wed Dec 31 06:48:47 PST 2025
Hi jim
As you have 4 battereis in series, you should use balancing devices between them. The kilovaukt are very susceptible to getting out of balance between batteries.
I had to work with a customer to fix his kilovault battereis. Numerous failures which was traced back to broken balancers.
Victron make good ones.
Jay
> On Dec 30, 2025, at 9:39 PM, Jim Gowdy via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Does anyone have any experience with the Kilovault 2400 HLX 12v batteries. I have a customer that wants to hook up a generator to his system and go over programming on an outback system. I looked up this battery company and they don't have a website and their phone number didn't work so I assume the company is out of business. I found a manual and the specs state that the bulk charge time is 2 minutes per battery I assume. I'm still a rookie and learning the proper charging parameters for different kinds of batteries so any help would be appreciated. He hasn't given me much info, but apparently there are......
> -8 batteries on a 48v system. I assume the batteries are 2 strings of 4 batteries.
>
> -Outback FXR 30/48 inverter
>
> -Outback FM Charge Controller. He didn't say what size, but the assumption is 80a
>
> -MATE 3 controller
>
> -Solar....not known at the moment
>
> -Gasoline powered 120v output portable generator.....KW is unknown at the moment. *I don't like this, but it's what the customer bought.
>
>
> --
> Jim with Gowdy Electric
> Cambria, Ca 93428
> business 805 927 2630
> cell 805 975 5279
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list