[RE-wrenches] Midnite AIO Random Unexplained Shutdowns
Tyrone Houck
tyronehouck at gmail.com
Fri Dec 26 11:33:47 PST 2025
I recommend doing the v7 update and following the installation tips pdf.
With parallel inverters do the update onsite and clear the data/5 minute
shutdown per recommendation. With single inverters it works fine remotely
if you can keep internet on(I've just had the customer put it in bypass
until the update was finished). V7 also includes an arc fault firmware
update. V7 firmware has appeared to fixed this issue at the sites I've had
issues with. I have yet to have an unexplained shutdown at any of my sites
on v7. Hope that helps. It sure has helped me sleep better at night!
On Fri, Dec 26, 2025, 9:22 AM Maverick Brown via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I have the same issue, but a single inverter installation. It happened a
> few times at night.
>
> No log entry.
>
> Tech support suggested upgrading to version 7. I asked for release notes.
> I haven’t upgraded yet, I haven’t had time to go babysit it for the
> customer. I’ve been trying to train the customer to do it himself. (bypass
> mode, standby, etc. I did install a bypass switch and I also installed a
> bluetti battery on the router.)
>
> Release notes would be nice.
>
> Thank you,
>
> Maverick
>
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
> • Solar Commander Remote Power
> • SunFlow Systems Cathodic Protection
> maverick at mavericksolar.com
> 512-460-9825
>
>
>
> On Dec 26, 2025, at 10:53 AM, Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Hi all,
>
> I have two new systems experiencing random shutdowns anywhere from 48
> hours to 3 weeks apart. The inverters will simply shut off, going into
> standby with no power to the loads, and absolutely nothing in the fault
> logs. Turning them back on with the master inverter power switch or
> remotely with app restores normal operation for some random period of time
> before it happens again.
>
> Here are the similarities:
>
> -Parallel inverter systems (3 or 4 AIO)
> -Powerflo16 batteries, closed loop comms (80 kWh and 112 kWh)
> -Grid interactive systems with netmetering
> -Large PV systems with DC Coupled PV on each inverter
> -Shutdowns typically happen at night, early morning hours
> -Loads are low and nothing out of the ordinary on the load side happening
> at the time of shutdown
> -Confirmed no errant Neutral to Ground bonds that shouldn't be there
> -Proper installation of ferrite rings
> -AP Smart RSDs
>
> Differences:
> -Two different firmwares (but all firmware per site is the same per
> inverter). Updated at different times by Midnite tech support remotely
>
>
> Has anyone experienced anything like this, and if so, did you find a
> resolution?
>
> I have a call into Midnite and hope to make some progress on Monday. I'm
> seriously concerned, especially with one site that doesn't have a bypass
> (due to space constraints). I can't have these sites going down and cutting
> power to the homes!
>
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251226/da4c896e/attachment.htm>
More information about the RE-wrenches
mailing list