[RE-wrenches] Magnum 4024 PAE inverter w/ ARTR and AGS
Michael Morningstar
mjmorningstar at gmail.com
Sun Dec 14 17:14:56 PST 2025
I just encountered the same thing. I upgraded a clients Discover AES to a
Helios AES and after a few months what you are describing started to occur.
I came to the same conclusion and all I could offer my client was "looks
like no more AGS for you until we can upgrade to a Victron system.
On Sun, Dec 14, 2025 at 3:24 PM Chris Schaefer via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> G'day All,
>
> Came across something I haven't seen in the past and I have over 4 dozen
> PAE units out there. It has to do with the Max Run Time setting on the ARTR
> or RTR and the Magnum AGS unit. I normally set the Max Run Time (MRT) to 12
> hours. It has been my understanding that this MRT value comes into play
> when it sees the generator input. Then once the genny runs for say 4-6
> hours the AGS then tells the genny to stop. I've been under the
> assumption that once the genny stops, the MRT would reset back to zero to
> ready itself for the next time the genny runs. What is happening is that
> the MRT seems to be accumulating for each genny run and then of course once
> it hits the MRT value you get the "Fault Max Rn". I can't find anywhere in
> the literature about the MRT value resetting after the genny stops, but I'm
> confident that this is the case. Can anyone confirm my thought process on
> this one or has anyone seen anything like this before? Heading out tomorrow
> with a new ARTR.
>
> Your Friendly Neighborhood Solar Guy,
> Christopher-
>
> Chris Schaefer’s
>
>
> *Tel 585-229-2083 or Cell 585-748-1870 *
> *5115 S Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
> <http://www.solarandwindfx.com> ~ E-mail: chris at solarandwindfx.com
> <chris at solarandwindfx.com>*
>
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Michael Morningstar
Morningstar Electric Inc
PO Box 1494
Mount Shasta, CA 96067
530-921-0560
CSLB 1116835
mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251214/6c734499/attachment.htm>
More information about the RE-wrenches
mailing list