As Tyrone says, times may have changed, but I've always approached supply-side connections based on the type of supply I'm connecting to. In Vermont, we see two types of connections. One with four wires between the meter and the main service disconnect (L1, L2, N, G). In this configuration, we do not make a neutral/ground bond at the PV system disconnect because one was made at the meter.
The other is three wires between the meter and main service disconnect (L1, L2, N). In this configuration, we do make a neutral/ground bond at the PV system disconnect.
Also, if I recall correctly, the PV system is not considered a second service under the NEC. But smarter people than I may have more up-to-date information.
Thanks,
Will
________________________________
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Tyrone Houck via RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Thursday, October 23, 2025 11:01 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Tyrone Houck <tyronehouck at gmail.com>
Subject: [EXTERNAL] Re: [RE-wrenches] N-G bond for supply side connection Midnite Power
CAUTION: This email originated from outside of the organization. Do not click links or open attachments unless you recognize the sender and know the content is safe.
My interpretation, and the way it was explained to me by both Ryan Mayfield and Kyle Bolger(several years ago at this point, popular opinion may have changed since). Is that it is not a seperate service.
It is however required to have a ground-neutral bond( though in my opinion pointless and redundant as there is a bond in the enclosure where the tap is made). If it gives you any issue, ensure as close to equal potential to the grounding electrode as possible(and make sure your neutral is appropriately sized). I personally don't see the point but it is an NEC requirement
On Thu, Oct 23, 2025, 6:08 AM Dave Tedeyan via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
Hi All,
For years I have understood that when doing a supply side connection, you are supposed to bond the neutral to ground in the solar service disconnect. I have a Midnite AIO system with two inverters (set up as a supply side connection) that recently was getting a CA-DC link Overvoltage error. When talking to Midnite, their first response was to make sure that there was only one N-G bond in the whole system. When I mentioned that the solar is a separate service and thus there is a N-G bond in both the main panel and the inverter distribution panel, they said to remove it from the inverter distribution panel. I want to make the system work right, but I also am hesitant to do something against how I have understood the NEC to be for a long time. I am curious if you all have thoughts on this or run into a similar situation.
Cheers,
Dave
--
[Logo]<https://urldefense.com/v3/__https://www.sungineersolar.com/__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM7l27rFH$>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd.<https://urldefense.com/v3/__https://www.google.com/maps/search/1653*Slaterville*Rd.**D7C**AIthaca,*NY*14850?entry=gmail&source=g__;KysrwqArJcKgKys!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM4tZUfh6$> <https://urldefense.com/v3/__https://www.google.com/maps/search/1653*Slaterville*Rd.**D7C**AIthaca,*NY*14850?entry=gmail&source=g__;KysrwqArJcKgKys!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM4tZUfh6$> | Ithaca, NY 14850<https://urldefense.com/v3/__https://www.google.com/maps/search/1653*Slaterville*Rd.**D7C**AIthaca,*NY*14850?entry=gmail&source=g__;KysrwqArJcKgKys!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM4tZUfh6$>
w: www.sungineersolar.com<https://urldefense.com/v3/__http://www.sungineersolar.com/__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pMwaujZYw$>
c: (607) 270-0370
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM44nwc7n$>
List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM_TSO_MP$>
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM214HEdk$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pM9SAWGzk$>
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pMxgahljj$>
Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!cfCkA7tAgtw29oHcZgoFLPG0fYrtoep5hMrKhWU7oKhftyB0eQP_x5leI3wGe5PYBW9joTZSqb8HdY4mSW7c6u6pMz1fDKvi$>
________________________________
Please be advised that this email may contain confidential information. If you are not the intended recipient, please notify us by email by replying to the sender and delete this message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20251023/28f9f09b/attachment.htm>
More information about the RE-wrenches
mailing list