I always use breakers more because they are easy to reset and visible if tripped. And if a class T fuse blows, you don’t actually know it and then you have the situation of having to go out to replace a $100 fuse or have the customer replace a fuse with live ends which I stopped doing a long time ago.
I wonder if midnite power is going to build a combiner box with breakers. I’m sure the breakers used in their batteries are way less expensive than the big 250’s we have used. I’d sure like to see one.
A question on the Class T fuses. Is it UL ok to mount the fuses not in a fuse holder? Like to a buss bar?
jay
> On Jul 16, 2025, at 5:23 AM, Jason Szumlanski via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
> I like the Midnite 1000/2000A battery combiners for this purpose. The 250A DC breakers are not cheap, but they add a level of convenience and protection that I think it worthwhile.
>
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
>
> On Tue, Jul 15, 2025 at 1:36 PM William Miller via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>> Kirk:
>>
>> First of all, I apologize for the typo in the subject line. I fixed it. I take my writing seriously but sometimes my devices fight me with autocorrect.
>>
>> You make good point regarding a scenario with a battery combiner. Relying on multiple BMSs for OCP would be a bad choice.
>>
>> Fortunately some cabinets come with breakers and those should be sufficient.
>>
>> William Miller
>> Miller Solar.com
>> 805-438-5600
>> www.millersolar.com <http://www.millersolar.com/>
>>
>>
>> On Tue, Jul 15, 2025 at 9:50 AM Kirk Herander <kirkh at vermont.solar> wrote:
>>> Hello William-
>>>
>>> I agree with your approach.
>>>
>>> I never historically have OCPD'ed lead acids at both ends of the battery cable run, but do now, esp. with high kwh LFP, where a DC combiner is in use.
>>>
>>> For instance, I had to design a 2000 ADC bus @ a nominal 55 vdc, for a 500 kwh Blue Ion LFP bank. To create enough space for cables and fuses, I started with -2- 2000A Midnite combiners, using one for positive and one for negative.
>>>
>>> Class T fuses are bolted directly to the DC bus (properly sized copper from copper.org <http://copper.org/> charts), and the BI BMS breaker protects at each respective battery cabinet.
>>>
>>> Same thing on the DC to inverter cables, class T's bolted to the bus, to its respective outback Radian, where the standard 175A breaker resides.
>>>
>>> I would never again do a building power system of any type or size without both ends of a power cable (point of use & point of origin) being protected, A best practice IMO.
>>>
>>>
>>>
>>> On Tue, Jul 15, 2025 at 1:13 AM William Miller via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>> Friends:
>>>>
>>>> When I design a lead-acid battery system I decide if I need over-current protection right at the battery or not. My logic is: if the leads are short, don’t go through a wall and are well protected, I can rely on OCPD in the BOS cabinets. If any of these criteria is a no I put appropriately rated class T fuses right at the battery.
>>>>
>>>> I’m thinking that since BMS devices have over-current protection baked-in, fusing at the battery would not be necessary for BMS equipped batteries in any case. Do you agree with that premise?
>>>>
>>>>
>>>> William Miller
>>>> Miller Solar.com
>>>> 805-438-5600
>>>> www.millersolar.com <http://www.millersolar.com/>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>
>>>
>>>
>>>
>>> --
>>>
>>>
>>> <>
>>> Kirk Herander / <>kirkh at vermont.solar <mailto:kirkh at vermont.solar>
>>> Owner|Principal, VT Solar, LLC
>>> Celebrating our 34st Anniversary 1991-2025!!
>>> dba Vermont Solar Engineering
>>> 802.559.1225
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250716/35bf4ec0/attachment.htm>
More information about the RE-wrenches
mailing list