[RE-wrenches] BMS as OCOD
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Tue Jul 15 12:52:47 PDT 2025
I agree as long as you have a long history with the battery/BMS. Since
all of this is so new or constantly changing I would add a class T as it
has a minor chance of being a failure item.
When I was testing this for Schneider, even they added the T fuse for
insurance as no-one had tested the internal T fuse and contactor. Cheap
insurance.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2025-07-14 10:12 pm, William Miller via RE-wrenches wrote:
> Friends:
>
> When I design a lead-acid battery system I decide if I need
> over-current protection right at the battery or not. My logic is: if
> the leads are short, don't go through a wall and are well protected, I
> can rely on OCPD in the BOS cabinets. If any of these criteria is a no
> I put appropriately rated class T fuses right at the battery.
>
> I'm thinking that since BMS devices have over-current protection
> baked-in, fusing at the battery would not be necessary for BMS equipped
> batteries in any case. Do you agree with that premise?
>
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com [1]
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
Links:
------
[1] http://www.millersolar.com
[2] http://members.sti.net/offgridsolar/
[3] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250715/f73cb2c9/attachment.htm>
More information about the RE-wrenches
mailing list