[RE-wrenches] 2020 705.12(E)

Jason Szumlanski jason at floridasolardesigngroup.com
Sun Jun 8 13:43:52 PDT 2025


I think the key phrase in 705.12(E) is "for such applications." They are likely
referring to grid-interactive inverters that are not configured as hybrid
inverters with grid-forming capability. You could install Sol-Arks that are
simply grid-tied with no batteries without using breaker hold-downs, but if they
use energy storage, that is a different "application."

For the load output of multiple Sol-Ark inverters, I do not believe there is any
requirement that each one lands on a circuit breaker. You can combine them with
a power distribution block or Polaris taps or other means, and land the combined
inverter output on a single circuit breaker that is fastened (if required,
depending on the application).


At least that's my reading of it.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Sun, Jun 8, 2025 at 1:55 PM Lou Russo via RE-wrenches
<re-wrenches at lists.re-wrenches.org> wrote:

> Aloha All,
> 
> 
> When combining the grid and/or load connections of multiple Sol-Arks does
> 705.12(E) mean we do not need breaker hold downs on back-fed breakers? The
> language is clear but I can't believe it is that easy!
> 
> 
> Aloha,
> Lou Russo 
> Spree Solar Systems LLC 
> C-34322
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org [http://re-wrenches.org]
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> [RE-wrenches at lists.re-wrenches.org]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> [http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org]
> 
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> [https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/]
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> [http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org]
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> [http://www.re-wrenches.org/etiquette.htm]
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org [http://www.members.re-wrenches.org]

[data:image/gif;base64,R0lGODlhAQABAIAAAP///wAAACwAAAAAAQABAAACAkQBADs=3D]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250608/93981f83/attachment.htm>


More information about the RE-wrenches mailing list