[RE-wrenches] [EXTERNAL] Re: Midnite AIO Generator Functionality

White, Will will.white at fluke.com
Tue May 13 10:08:22 PDT 2025


I just installed a Victron/Discover system at my house. The install went well, although, like Michael said, it needs some customization to work with conduit.

Tech support is done through your dealer. I bought through Kienan Maxfield (he's on the list), and his support was excellent.

The comms does take some work to set up with three apps between the two vendors, but once it's set up, it's worked without an issue.

You do need to hardwire the display, which prevents installing it at a significant distance, but you can do anything on the display in the app, which was a huge improvement from my Outback VFX system.

Thanks,
Will
________________________________
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf of Michael Morningstar via RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Tuesday, May 13, 2025 11:53 AM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Michael Morningstar <mjmorningstar at gmail.com>
Subject: [EXTERNAL] Re: [RE-wrenches] Midnite AIO Generator Functionality


CAUTION: This email originated from outside of the organization. Do not click links or open attachments unless you recognize the sender and know the content is safe.



I've had good luck with the Victron/Discover pairing for small off-gridsystems. The drawbacks are: No tech support (as far as I know), requires stacking for 120/240 and more than 3kw, no conduit boxes on MPPTs, lots of BOS components, and lots of comms and a familiarity with the various comms cables. Also, I haven't come up with a reliable solution for installing the touch screen at distance from the power system. That is system in a power shed remote from the dwelling.

I've had zero issues with this pairing and it will probably be my go to for awhile. We're installing our first AIO offgrid in a few days, as I purchased the equipment for the project early last fall when they were first released, not realizing their unsuitability for off-grid.

It's weird, I would have expected better from Midnite and wonder just WHO engineered the unit?

Generators: Simple diesel genset 1st choice always or liquid cooled/low RPM LPG for 20kw up, Honda eu7000is w/ LPG conversion for smaller requirements


On Tue, May 13, 2025 at 7:50 AM MDElectricSolar via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
After having many many failures very prematurely with the Kohler 14 and 20s I've switched to the Cummins-Onan air cooled two wires start units and they have been flawless so far.

Michael D Nelson
MD Electric & Solar, Inc.
707-684-0064 mobile
707-884-1862 office
www.mdelectricsolar.com<https://urldefense.com/v3/__http://www.mdelectricsolar.com__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9WoL-WB$>
www.facebook.com/mdelectricandsolar<https://urldefense.com/v3/__http://www.facebook.com/mdelectricandsolar__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_FxclufRm$>


On May 13, 2025, at 7:33 AM, Mac Lewis via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:


Hello Jay,

I am using Kohler 14 RCAs in Colorado.  It has the off-grid warranty 18-month/1000 hr.  I have seen good results, I probably have 60-70 out there now.  If you can make it through the 6 month mark, its probably going to be pretty good machine (control and /or sensor failures).  I have had random issues, they aren't perfect, but its the best I've come across for an autostart machine that works well with elevation derate here.  Very simple to troubleshoot, stepper motor, controller, not much else.  Btw, Kohler sold its residential line to Rehlko recently so who knows!



On Tue, May 13, 2025 at 8:21 AM Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
I’ve installed one. It works and simple
Like the other AIOs.
It has a different firmware/display than the 8,12 kw units which is a bit frustrating.

The main drawback with the 6 is it’s only 3kw per leg. It doesn’t like being too out of balance either. Tare loss is a bit high and the fans seems to run a lot but better cooler than hotter.
But it’s less than 1/2 the price of the 8kw. It’s about $1600.
If you just bought it as a CC it’d be a great deal.

As to it not being made in China I think is nothing more than simantics.
It might now be assembled in Texas but the parts are all made in China.
So draw your own conclusions



On May 13, 2025, at 6:10 AM, Drake Chamberlin via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:



Talking to Steve at Zonna about the problems with off grid equipment, he recommended the EG4 6000XP as a good off grid inverter. He said they are no longer made in China and are a very good product. Does anyone have experience with that unit?

Thanks,

Drake


Drake Chamberlin

Athens Electric LLC

Ohio Electrical Contractor’s License 44810

NABCEP Certified PV Installation Professional

---



On 2025-05-12 13:11, Ray Walters via RE-wrenches wrote:

So the bypass switch gets the house power on, and I too always recommend a hard bypass switch. However, you still need a 48 v power supply to get the battery system back up, and that's becoming a serious pain in my aging backside.  Until AIOs with Li+ batteries, lead acid would have enough voltage to get the charge controller to come back on, and eventually the customer could get the inverter back on too.  No special trip out.

We need an independent circuit that would sense array voltage, and wake up the battery, so it could take a charge: a backup battery for the offgrid battery.  Without that, AIOs and Li+ batteries are not self healing like Lead Acid.  We are going backwards fast, but with an amazing amount of new Chinese technology driving the jalopy in reverse.  (Danger Will Robinson)

Ray Walters
Remote Solar

On 5/12/2025 10:54 AM, Jason Szumlanski via RE-wrenches wrote:
We always recommend a transfer switch to bypass the inverter and send generator power to the loads. Most clients take us up on it. For retrofits, sometimes there can be space limitations, however.

As for the function of the AIO, there is no integrated mechanical bypass, and since there is an internal relay controlling the generator input (or smart load output on that breaker), I think the default function is for the relay to open when the inverter turns off. AC voltage on the load side of the breaker does not close the relay and turn the inverter back on automatically.

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208

On Mon, May 12, 2025 at 9:49 AM Dave Angelini Offgrid Solar via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
All sounds wrong to me. Call Midnite.

Typically there is a AC bypass mechanical switch that allows the gen to bypass the inverter and power loads.




Dave Angelini Offgrid Solar
"we go where powerlines don't"
  <https://urldefense.com/v3/__http://members.sti.net/offgridsolar/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_FxN20-Dy$> https://offgridsolar1.com/<https://urldefense.com/v3/__https://offgridsolar1.com/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9des9dS$> <https://urldefense.com/v3/__http://members.sti.net/offgridsolar/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_FxN20-Dy$>
e-mail  offgridsolar at sti.net<mailto:offgridsolar at sti.net>
text 209 813 0060


On 2025-05-12 9:29 am, Jason Szumlanski via RE-wrenches wrote:

Maybe I'm missing something, but it seems like there is a flaw in the logic for how generator integration works with this product. Unlike some of the other AIOs, you can't put the generator on the Grid input in an off-grid scenario. You have to use the Generator smart load breaker, which isn't a dedicated generator input, but a programmable circuit. This is problematic because it seemingly has a normally open internal relay that closes only when the inverter is ON. At least, that's how it seems to work in my limited experience.

Why is this a problem? If the battery capacity drops below the low voltage cutoff, the inverter turns off. You have to turn the inverter ON for the generator relay to close so you can charge the battery, but since the battery is too low, the inverter won't turn on. You would have to reprogram the inverter to drop the cutoff voltage/SOC below the current battery state. For people who do not want to use AGS, or if AGS fails to start the generator for any reason, getting the generator to charge the battery manually is no easy task.

Moreover, turning the generator on manually when the inverter is in an OFF state will not pass power to the loads, and will not turn the inverter ON automatically. You have to get the inverter turned ON somehow so that the generator power can pass through to the loads. And since the startup sequence for this inverter is very quirky, non-intuitive, and unreliable, that makes the problem even worse. I'm not sure if you can even turn the inverter ON when there is generator input and the battery is too low. I don't think you can because the relay is open and the inverter doesn't even see generator voltage when it is in an OFF state.
This seems like a serious oversight and a reason to go with one of the other AIOs on the market. I believe the Sol-Ark 15K and EG4 18kPV will both immediately power loads and start charging when the generator is on, regardless of whether the generator is connected to the Grid or Generator input. Any AC input immediately passes through to the loads. This is because those inverters stay "on" when a low battery condition is met, and they simply stop using the battery to invert power if the battery conditions do not allow it, based on the settings.

The logic of the Midnite AIOs turning "off" when battery cutoff is met and opening the generator relay doesn't make sense to me. Am I wrong about how this works?

Jason Szumlanski
Principal Solar Designer
Florida Solar Design Group



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>




_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>



--



Mac Lewis


"Yo solo sé que no sé nada." -Sócrates

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<https://urldefense.com/v3/__http://re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F9SgmqL0$>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F1jdmJcx$>

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/<https://urldefense.com/v3/__https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F34t_ccL$>
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<https://urldefense.com/v3/__http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F7TvKUVb$>

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm<https://urldefense.com/v3/__http://www.re-wrenches.org/etiquette.htm__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F5ZIJPUP$>

Check out or update participant bios:
http://www.members.re-wrenches.org<https://urldefense.com/v3/__http://www.members.re-wrenches.org__;!!KPww_GFiJXw!ds1sCxiotFVibSVNrnrNKq59kyU2SV0dI8FJjvOR10z8GFNqHn2C4cZCe866QInKpWKQl0GBlhnywymC9lPruDQ_F-5noG-f$>



--

Michael Morningstar


Morningstar Electric Inc

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

CSLB 1116835

mjmorningstar at gmail.com<mailto:mjmorningstar at gmail.com>


________________________________

Please be advised that this email may contain confidential information. If you are not the intended recipient, please notify us by email by replying to the sender and delete this message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250513/8e9943cb/attachment.htm>


More information about the RE-wrenches mailing list