[RE-wrenches] Radian - Mate 3 incorrect high voltage reading

drake.chamberlin at redwoodalliance.org drake.chamberlin at redwoodalliance.org
Wed Apr 9 10:04:40 PDT 2025



For a followup, it appears that the problem was in a ribbon cable 
connection. After checking the power wiring and starting the inverter 
again, the problem still remained.

Then, I disconnected and reconnected the ribbon cables at both ends. On 
restart, the voltage was with 6 V of the multi meter reading. I adjusted 
this out with the offset in the calibration menu. The voltage has read 
steady for a day now.

Thank you!

Drake

Drake Chamberlin
Athens Electric LLC
OH Electrical Contractor License 44810
NABCEP Certified Solar PV Installation Professional
740-856-9648

---

On 2025-04-06 09:25, Mac Lewis via RE-wrenches wrote:

> Also look for loose connections and corrosion.  If it tries to push 
> current and the voltage rapidly rises, it can indicate resistance 
> somewhere.
> 
> Good luck!
> 
> On Sun, Apr 6, 2025 at 7:20 AM Maverick Brown via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> Maybe the Calibrate setting got changed somehow.
> 
> OpticsRE: Device Map, Inverter, Calibrate.
> 
> From the Mate: Lock, 141, Settings, Inverter, Calibrate.
> 
> Make sure the settings are Zero offset or at least appropriate.
> 
> Thank you,
> 
> Maverick
> 
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
> * Solar Commander Remote Power
> * SunFlow Systems Cathodic Protection
> maverick at mavericksolar.com
> 512-460-9825
> 
> On Apr 5, 2025, at 1:22 PM, Drake Chamberlin via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> A Radian 4048 disconnected from the grid with a high grid voltage error 
> showing on the Mate 3. The Mate 3 was displaying a voltage of 279 - 280 
> V. The Mate 3 was replaced with another Mate 3, and the high voltage 
> reading remained.
> 
> When the voltage was checked with two separate multi meters, the 
> readings came out to 249 - 250 V. I believe that the 249 - 250 volt 
> reading is correct.
> 
> The incorrect, high voltage reading seems to be coming for the 
> inverter, not the Mate 3, since two Mates were used.
> 
> Has anyone experienced this?
> 
> What could be the cause and solution to the problem?
> 
> Thank you,
> 
> Drake
> 
> Drake Chamberlin
> Athens Electric LLC
> OH Electrical Contractor License 44810
> NABCEP Certified Solar PV Installation Professional
> 740-856-9648
> 
> --
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

   --

   Mac Lewis

"Yo solo sé que no sé nada." -Sócrates
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250409/2e77f997/attachment.htm>


More information about the RE-wrenches mailing list