[RE-wrenches] Battery Conductors and the NEC
Chris Sparadeo
sparadeo.chris at gmail.com
Thu Mar 20 10:09:24 PDT 2025
Hey everyone,
I’m looking for some clarification on conductor ampacity ratings as they
relate to battery cables. My understanding is that the term ‘free air’
wasn’t actually defined in the NEC until 2020 and that conductors installed
in a nipple, wire trough, conduit body, or enclosure don’t qualify as ‘free
air.’ That said, I’ve noticed some battery manufacturers and installers
seem to be applying Table 310.17 (free air) rather than 310.16 (raceway)
when specifying conductor sizes—particularly for battery-to-inverter
connections.
For example, a battery manufacturer offers a 48Vdc LFP battery with 10kW
continuous output, which would suggest needing a conductor rated for ~245A
(safety factor included). However, they provide a wire trough for the
battery to inverter connection and provide a 1/0 Cu battery cable. This
seems undersized if 310.16 applies. Am I overthinking this, or are these
configurations typically tested and listed accordingly?
I see similar situations across multiple manufacturers, and while I don’t
put too much trust in marketing images, I noticed SimpliPHI using a single
1-1/4” conduit from a stack of 6.6 batteries to a 15kW inverter, which also
raises questions. Is there a code-compliant rationale I’m missing, or are
manufacturers and installers misapplying Table 310.17? I spoke with one
applications engineer that referenced table 310.17 as the “battery cable
table”. I get the value of running free aired battery cables with regard to
ampacity allowance, but I also see the value in protecting energized
conductors in a raceway. Would love to hear your insights!
Best,
Chris Sparadeo
C_802-369-4458