[RE-wrenches] Arc Fault problem in FM100
Dana Orzel
dana at solarwork.com
Sat Mar 8 08:32:01 PST 2025
Pull the ground jumper in the FM100.
Double check all terminal connections in the Power center related to the FM100. Do the pull test carefully,
I once missed tightening a neutral that was passing current & then not. I finally heard a slight crackle sound as I turned the array input & battery breaker at the same time to on, did the pull test [moved wires & the Fm100 lite up], then Felt like an idiot! Tightened the neutral & all good.
_________________________________________________________
Dana Orzel GREAT SOLAR WORKS!
C - 208.721.7003 E - dana at solarwork.com<mailto:dana at solarwork.com>
W - www. greatsolarworks.com www.solarwork.com<http://www.solarwork.com/>
"Responsible Technologies for Responsible People since 1988!"