[RE-wrenches] Tigo inverter experience
Bradley Bassett
bbassett2 at gmail.com
Sat Feb 15 07:44:09 PST 2025
You asked... the IMO FireRaptors I've installed seem to be completely
reliable since they have their own separate 24VDC activation circuit. I do
kind of like that the circuits are dead while working on them, but the
extra wiring is of course more work. There is a huge amount of wire mgmt to
do since the leads are all 6ft long, both the PV output circuits and the
24VDC activation circuits. Best is the fact that they work on ANY charge
control or inverter. With older modules like my REC260's you can put two
modules per FireRaptor.
It would be fine by me if RSD was no longer a requirement.
Doesn't Tesla have a UL listing for array level RSD now?
BTW the AP smart does not work with Classic charge controllers.
On Sat, Feb 15, 2025 at 6:07 AM david quattro via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> RSD is the worst thing to happen to solar. Has anyone considered civil
> disobedience?
> I wonder what would happen if all the installers banded together and
> refused, as a united industry ‘brotherhood.’ WE are the ones stuck with the
> bullshit in the aftermath.
> I’m not being snarky here , this a genuine question to the group:
> Does anyone have *good* experience with RSD? i.e. you’re really glad
> RSD was there, and you genuinely feel safer? you’re glad and happy to
> comply with this code and you look forward to continuing to use RSD for the
> rest of your career?
>
>
>
>
> On Fri, Feb 14, 2025 at 3:40 PM Ray Walters via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> it seems silly that we are required to install these extra pieces of
>> equipment for added "safety", that are actually a fire hazard on the roof.
>> Just to survey again: how many homes have been saved by RSD? How many fire
>> fighters have actually actuated the RSD system, so that they could hack
>> through the array to vent the roof?
>>
>> I think it should only be required if you have covered so much of the
>> roof with PV, that the fire dept can't access uncovered roof to do their
>> venting. The whole premise of RSD is flawed. IMHO, its just another
>> effort to block the wider adoption of solar.
>>
>> When it comes to off grid, RSD causes such a decrease in reliability to
>> amount to a decrease in safety, due to possible loss of communications,
>> water, and heat. Add the fire hazard and RSD is really not making our
>> customers' lives better.
>>
>> Ray Walters
>> Remote Solar
>> On 2/14/2025 3:52 PM, Jason Szumlanski via RE-wrenches wrote:
>>
>> I had a site (not my install) with a ground rack and these TS4-F units,
>> and they exhibited the exact same burn characteristics. At least half of
>> them were burned up to some degree.
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Fri, Feb 14, 2025 at 2:11 PM David Buckner via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Hello Nick,
>>>
>>> Yes, it's the TS4-F units. We have made every effort to install to the
>>> specs provided (as the goal post and solutions keep changing) but have
>>> still seen RSD's start to swell and/or burn over time. We've separated DC
>>> wires and home runs and stayed within the home run complete circuit
>>> distance that is recommended. We've used the "Pure Signal" transmitter
>>> solution that syncs up the signaling from multiple inverters in an effort
>>> to avoid the "chatter" that starts when the RSD is failing (see video below
>>> about that).
>>>
>>> It's all field R&D at our expense in my opinion. Sadly, I'd be happy if
>>> the RSD failed and didn't work but it starts to work in overdrive until it
>>> burns up and causes an arc. These photos below are from a site where we
>>> got lucky and the fire didn't spread. Below the photos is a link to a
>>> video of Tigo and Mayfield discussing the crosstalk issue.
>>>
>>>
>>>
>>>
>>>
>>> Here is a video discussion of the cross-talk and signal corruption
>>> issues that are the supposed cause of the unit's failure's:
>>> https://www.youtube.com/watch?v=L_1_0Ofuhao
>>> <https://www.youtube.com/watch?v=L_1_0Ofuhao>
>>> Mayfield Renewables and Tigo Energy - Crosstalk Workshop
>>> <https://www.youtube.com/watch?v=L_1_0Ofuhao>
>>> A deep dive into how to design PLC (Power-Line Communication) based
>>> solar rapid shutdown systems in order to minimize cross-talk and other
>>> signal integrity issues. This is a technical presentation meant to assist
>>> with the design of large scale solar rooftop arrays that use PLC-based
>>> rapid shutdown systems, which are used to meet the rapid ...
>>> www.youtube.com
>>>
>>>
>>> David Buckner
>>>
>>> President
>>>
>>> 917-848-0215
>>>
>>> 718-389-1545
>>>
>>> 41 Box Street 2nd Floor, Brooklyn, NY 11222
>>> ------------------------------
>>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
>>> behalf of Nick Lucchese via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org>
>>> *Sent:* Friday, February 14, 2025 1:26 PM
>>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>> *Cc:* Nick Lucchese <lucchesesolar at gmail.com>
>>> *Subject:* Re: [RE-wrenches] Tigo inverter experience
>>>
>>> CAUTION: External Email.
>>> Greetings David,
>>>
>>> Can you elaborate on which products of theirs failed catastrophically?
>>> Their TS4-F single and double units by chance? My experience has been an
>>> annoying occurrence where certain installed units lock up
>>> requring replacement after the array is shut down for O&M tasks but nothing
>>> that starts burning as you mentioned. I've still got a reasonable amount of
>>> them in my inventory but would rather not deploy if they're "burning" in
>>> some way.
>>>
>>> Thanks for sharing your experience, Nick
>>>
>>> *We've had catastrophic failures with the RSDs and have heard from
>>> plenty of others that have had the same. The company denies and deflects
>>> and blames the installer until you are fatigued. A product that uses power
>>> line communication that can start burning when the signal gets corrupted
>>> should not be allowed to remain on the market.*
>>>
>>> *David Buckner*
>>> *SES*
>>>
>>>
>>> David Buckner
>>>
>>> President
>>>
>>> Solar Energy Systems
>>>
>>> 917-848-0215
>>>
>>> 718-389-1545
>>>
>>> dbuckner at solaresystems.com
>>>
>>> www.solaresystems.com
>>> <https://us.content.exclaimer.net/?url=https%3A%2F%2Fwww.solaresystems.com%2F&tenantid=sjl0rdWaEe6F-WBFvdNAXQ&templateid=933619bad6e2ee11aaf06045bdd55b16&excomponentid=W0znjuLBICxfJOZwpEisk1w6Uz7kRcz8RFh31bsCZu4&excomponenttype=Link&signature=oLHGWCDHeQYPxuVijopczXguVIz2A9gWA29emAtwvdbqV2XsAnsbVfPJR3OQHtcxck-4zeNWEHrxwAX_LXCUOBXnvLDZkSB3Ue09sLzQcUNKGxMLclBt5peel7iiM1neHKnk8UctTRnOeUfIagifjZaGWicP4Wi23eUaL-JSNh0iUlYWH5Y2kOEt_QGU-R6LtdhPzR8aNOqjq8ttGuksaSFX3YQorUNiBDkXDGXmmCSiiNgljGMekvYiEvoXMsCe_CC1DpnfHsaH45ZBD8L442uACHbkOuyDJ-IG20zpBYXGK3TzDh-GW4efLwZfi6MUcJohrIgQQag5JDhSynWoDQ&v=1&imprintMessageId=70f4909c-5e4b-4d4e-a4f1-8a28a937dd26>
>>>
>>> 41 Box Street 2nd Floor, Brooklyn, NY 11222
>>>
>>> On Thu, Feb 13, 2025 at 6:06 PM David Buckner via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>> We've had catastrophic failures with the RSDs and have heard from plenty
>>> of others that have had the same. The company denies and deflects and
>>> blames the installer until you are fatigued. A product that uses power
>>> line communication that can start burning when the signal gets corrupted
>>> should not be allowed to remain on the market.
>>>
>>> David Buckner
>>> SES
>>>
>>>
>>> David Buckner
>>>
>>> President
>>>
>>> Solar Energy Systems
>>>
>>> 917-848-0215
>>>
>>> 718-389-1545
>>>
>>> dbuckner at solaresystems.com
>>>
>>> www.solaresystems.com
>>> <https://us.content.exclaimer.net/?url=https%3A%2F%2Fwww.solaresystems.com%2F&tenantid=sjl0rdWaEe6F-WBFvdNAXQ&templateid=933619bad6e2ee11aaf06045bdd55b16&excomponentid=W0znjuLBICxfJOZwpEisk1w6Uz7kRcz8RFh31bsCZu4&excomponenttype=Link&signature=oLHGWCDHeQYPxuVijopczXguVIz2A9gWA29emAtwvdbqV2XsAnsbVfPJR3OQHtcxck-4zeNWEHrxwAX_LXCUOBXnvLDZkSB3Ue09sLzQcUNKGxMLclBt5peel7iiM1neHKnk8UctTRnOeUfIagifjZaGWicP4Wi23eUaL-JSNh0iUlYWH5Y2kOEt_QGU-R6LtdhPzR8aNOqjq8ttGuksaSFX3YQorUNiBDkXDGXmmCSiiNgljGMekvYiEvoXMsCe_CC1DpnfHsaH45ZBD8L442uACHbkOuyDJ-IG20zpBYXGK3TzDh-GW4efLwZfi6MUcJohrIgQQag5JDhSynWoDQ&v=1&imprintMessageId=70f4909c-5e4b-4d4e-a4f1-8a28a937dd26>
>>>
>>> 41 Box Street 2nd Floor, Brooklyn, NY 11222
>>>
>>> The information contained in this email message, including any attached
>>> files transmitted, is confidential and may be legally privileged. It is
>>> intended for the sole use of the individual(s) named above. If you are the
>>> intended recipient, be aware that your use of any confidential or personal
>>> information may be restricted by state and federal privacy laws. If you,
>>> the reader of this message, are not the intended recipient, you are hereby
>>> notified that you should not further disseminate, distribute or forward
>>> this email message. Email transmission cannot be guaranteed to be secured
>>> or error-free as information could be intercepted, corrupted, lost,
>>> destroyed, arrive late or incomplete, or contain viruses. The sender
>>> therefore does not accept liability for any errors or omissions in the
>>> contents of this message, which arise as a result of this e-mail
>>> transmission. If you have received this email in error, please notify the
>>> sender and immediately delete the material from your computer system. Thank
>>> you.
>>> ------------------------------
>>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
>>> behalf of Howie Michaelson via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org>
>>> *Sent:* Thursday, February 13, 2025 7:05 PM
>>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>>> *Cc:* Howie Michaelson <Howie.Michaelson at gmail.com>
>>> *Subject:* Re: [RE-wrenches] Tigo inverter experience
>>>
>>> CAUTION: External Email.
>>> I do not have a lot of experience with Tigo equipment, almost all using
>>> their optimizers with CCAs and TAPs. The 2 things I can say is after
>>> getting my head wrapped around the setup and commissioning process (which
>>> is not the most intuitive process), I haven't had much trouble with them
>>> (again only have maybe 4 or 5 systems out there), and their tech support is
>>> generally very available and very knowledgeable and helpful, impressively
>>> so. Otherwise I can't speak much to their durability, reliability, or
>>> functionality.
>>>
>>> Howie Michaelson
>>> Sun Catcher
>>>
>>>
>>> On Thu, Feb 13, 2025 at 6:50 PM Vince McClellan via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>> Hi Dave
>>> I haven't tried their micro inverter or ESS, but so far all the products
>>> that I've used from Tigo including the RSD switches that melted have been
>>> problematic. Personally, I wouldn't use their products.
>>>
>>>
>>> Vince McClellan
>>>
>>> President
>>>
>>> NABCEP PV Professional
>>>
>>> p: 541-485-8122
>>>
>>> a: 860 Conger St. Suite 12,. Eugene, OR 97402
>>> <https://www.google.com/maps/search/860+Conger+St.+Suite+12,.+Eugene,+OR%0D%0A++++++++++++++++++++++++++++++++++++++++++++++++97402?entry=gmail&source=g>
>>>
>>> e: vince at solarenergydesign.com <vince at solarenergydesgin.com>
>>>
>>> w: SolarEnergyDesign.com
>>>
>>> CCB# 161672
>>>
>>>
>>>
>>> If you have received this email and are not the intended recipient,
>>> please delete this email. Copying or using any part, content, or attachment
>>> of this email is strictly prohibited.
>>>
>>>
>>>
>>> On Thu, Feb 6, 2025 at 10:53 AM Dave Tedeyan via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>> Hi All,
>>> I am curious if anyone has any experience with the Tigo inverter and
>>> energy storage system. It looks very similar to the SMA setup, but maybe a
>>> bit farther along in development. Even as just a simple string inverter, it
>>> seems fairly reasonably priced.
>>>
>>> Cheers,
>>> Dave
>>>
>>> --
>>>
>>> [image: Logo] <https://www.sungineersolar.com/>
>>> Dave Tedeyan, P.E.
>>> Owner | Sungineer Solar
>>> p: he | him | his
>>> a: 1653 Slaterville Rd.
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>>
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>| Ithaca,
>>> NY 14850
>>> <https://www.google.com/maps/search/1653+Slaterville+Rd.+%C2%A0+%7C%C2%A0Ithaca,+NY+14850?entry=gmail&source=g>
>>> w: www.sungineersolar.com <http://www.sungineersolar.com/>
>>> c: (607) 270-0370
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> <http://www.re-wrenches.org/etiquette.htm>
>>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image386447.png
Type: image/png
Size: 608 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image228829.png
Type: image/png
Size: 402 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 387727 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image864144.png
Type: image/png
Size: 40037 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 367791 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image074443.png
Type: image/png
Size: 804 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0019.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 437677 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0020.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-hl1uetzc.jpg
Type: image/jpeg
Size: 18160 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image421967.png
Type: image/png
Size: 608 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0021.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 443090 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0022.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image157869.png
Type: image/png
Size: 40037 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0023.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image947377.png
Type: image/png
Size: 499 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0024.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image717129.png
Type: image/png
Size: 596 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0025.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image851251.png
Type: image/png
Size: 596 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0026.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image016112.png
Type: image/png
Size: 402 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250215/6b7b652e/attachment-0027.png>
More information about the RE-wrenches
mailing list