[RE-wrenches] neutral ground bond in EG4
jay
jay.peltz at gmail.com
Tue Dec 10 14:59:37 PST 2024
I just got an email back from them saying the following.
There is no solid bond but the following will allow voltage to be detected between neutral and ground.
Internal EMI filters or transient suppression devices that connect the AC lines to the ground.
A small leakage path to ground via these components, which can result in measurable voltage.
Is this common with other brands such as sol ark or midnite?
thanks
jay
> On Dec 10, 2024, at 2:38 PM, jay <jay.peltz at gmail.com> wrote:
>
> Hi All
>
> I just got off the phone with EG4 with the following situation and I wonder if anyone has see this or can comment.
>
> With no wires attached, inverter ( LUX 6000XP) I read 120v from L1 to ground and of course 120v to N. Yes it has an internal ground bond option which is turned off.
>
> EG4 says this is normal go ahead and wire it up and that it’s fine that the main panel some 15’ away is where that bonding is officially happening. As I was worried that I was going to have 2 ground/neutral bonds.
>
> I’ve not seen this with our legacy inverters, could this be some kind of a non solid connection??
>
> I wonder if this is common with these types of inverters?
>
> thanks in advance.
>
> jay