[RE-wrenches] More Issues with Parallel Sol-Ark 15K System

Lou Russo lou at spreesolarsystems.com
Fri Nov 15 09:05:03 PST 2024


Most of our residential off-grid systems are designed around the peak load
so a lot of the time there is extra capacity laying around. I assumed the
fault logic was similar to what Jason is suggesting, 1 inverter faults and
drops out then the remaining "higher level" inverters run and fault on AC
overload if the situation requires it. Guess I thought wrong.

Aloha,

Lou Russo
Owner
lou at spreesolarsystems.com
Office - 808 345 6762
Spree Solar Systems LLC
CT-34322



On Fri, Nov 15, 2024 at 6:37 AM Sam Haraldson via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> ...I don't see how that would put at risk "safeguarding the customer’s
>> investment."
>>
>
> Jason, my understanding of the risk is the system is designed to output an
> amount of power greater than or equal to the load requirements.  If one or
> more of the inverters fault but the load requirements remain the same the
> functioning inverters are not capable of meeting that demand.  Someone
> please correct me if my understanding of that is wrong.
>
> - Sam
>
>
> [image: OnSite Energy]
> <https://www.google.com/url?q=https://onsiteenergyinc.com/&source=gmail-html&ust=1677085494759000&usg=AOvVaw2NN36GoM1sjnS4RdC8Svt->
>
> SAM HARALDSON
> Operations Specialist
> (406) 551-6135
> 1515 N. Rouse Ave Bozeman, MT 59715
> Locally owned and operated since 2012
> [image: B Corporation] <https://onsiteenergyinc.com/bcorp>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241115/2fd6f486/attachment.htm>


More information about the RE-wrenches mailing list