[RE-wrenches] Sol-Ark Gen Input

rick at solshineenergy.com rick at solshineenergy.com
Tue Oct 15 12:03:27 PDT 2024


William,

There’s no PV on this system. It’s AC coupled to an SMA SB5.0. 

As a test, we turned off the Grid input, Load output, and turned off the battery breaker. As expected, the high voltage DC eventually bled to 0V. Turning things on in this order: Battery, Grid, then Load resulted in the high voltage appearing once the Grid relay kicked on. Actually, the high voltage ramped up slowly once the Grid relay turned on.

We’ve been installing these for years and have never seen this. Then again, we’ve never measured that point.

> On Oct 15, 2024, at 2:32 PM, William Miller via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Rick:
>  
> If I had to guess I’d say you have a PV wiring fault.  The PV positive may be shorted to ground.  
> This would make the inverter chassis negative in relation to ground.  
>  
> The logic I use is to ask what is the likely source of DC at 195 volts?  It is most likely the PV circuits, wouldn’t you say?
>  
> If the DC Fault is not eternal then it must be internal to the inverter.  This could be a dangerous situation.  I would proceed with caution.
>  
> Try completely isolating the PV from the inverter as a start.
>  
> Good luck.
>  
> William Miller
>  
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> CA Lic. 773985
>  
>  
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On Behalf Of rick--- via RE-wrenches
> Sent: Tuesday, October 15, 2024 11:09 AM
> To: RE-wrenches
> Cc: rick at solshineenergy.com <mailto:rick at solshineenergy.com>
> Subject: [RE-wrenches] Sol-Ark Gen Input
>  
> Back on the Sol-Ark topic again. We have a customer whose 12kW is measuring -195VDC to ground from L1 and L2 with the Gen breaker open. L1 to L2 = 0V. I know the Gen input can be configured as an output, but reading a high DC voltage to ground is concerning. The generator has never been run. System is operating normally. 
>  
> Anyone have a Sol-Ark accessible that could verify what they’re reading?
>  
> Thanks in advance. 
>  
> Rick Brown
> Solshine Energy 
> Solar Electric Contracting Services 
> www.solshineenergy.com <http://www.solshineenergy.com/>
> Roanoke, VA
> Office: 540.235.3095
> Mobile: 540.808.9502
> CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) named in
> 
> the message header. Unless otherwise indicated, it contains information that is
> 
> confidential, privileged and/or exempt from disclosure under applicable law. If you have
> 
> received this message in error, please notify the sender of the error and delete the
> 
> message. Thank you.
> 
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
> 
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergy.com
Roanoke, VA
Office: 540.235.3095
Mobile: 540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21

CONFIDENTIALITY NOTICE -- This email is intended only for the person(s) named in
the message header. Unless otherwise indicated, it contains information that is
confidential, privileged and/or exempt from disclosure under applicable law. If you have
received this message in error, please notify the sender of the error and delete the
message. Thank you.”

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241015/01b26517/attachment.htm>


More information about the RE-wrenches mailing list