[RE-wrenches] Sol-Ark 15KW is rock steady, but crazy wild grid voltages when connected to grid
Blake Gleason
blake at sunlightandpower.com
Thu Sep 12 18:40:33 PDT 2024
Definitely sounds like a loose neutral on the utility side (likely at the
pole/tap).
I suspect if you turn off and disconnect the Sol-Ark the light flickering,
etc will continue (until the utility recrimps their neutral...)
Blake
On Thu, Sep 12, 2024 at 5:38 PM Scot Arey via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I have Sol-Ark 15KW with 31kwh battery has been installed for year+.
>
>
>
> Customer has for two days been having grid voltage issue seen as dimming
> lights. No neighbors reporting issues. He called his electrician who noted
> one high conductor and the other low. Have seen this before unrelated to
> solar and it was a bad neutral. His electrician says ok.
>
> Customer disconnects from the grid because the fluctuations so severe and
> when he does, voltage issues go away and Sol-Ark is rock steady at
> 120-volts per leg. I send my senior tech over to ensure we don’t have a
> loose neutral or any grid conductors to the grid input. Nothing found.
>
> Picture attached of grid voltages from the Sol-Ark monitoring (very
> helpful, I might add.)
>
> The electric cooperative is sending a tech out tomorrow. Any body have
> insight or history with this?
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Blake Gleason, PE | Employee Owner
Director of Innovation and Technical Excellence
O: 510-845-2997 x128
C: 510-867-5878
<http://www.sunlightandpower.com/>
<https://linktr.ee/SLP_Socials>
1035 Folger Ave.
Berkeley, CA 94710
www.sunlightandpower.com
License #326203
<https://benefitcorporationsforgood.com/> <https://www.amicussolar.com/>
<https://calssa.org/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240912/c99eee68/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 136365 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240912/c99eee68/attachment.png>
More information about the RE-wrenches
mailing list