[RE-wrenches] Neutral run to critical loads sub-panel
Jason Szumlanski
jason at floridasolardesigngroup.com
Tue Jul 30 05:48:56 PDT 2024
See 300.3(B). I think that's what you are looking for.
Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208
On Mon, Jul 29, 2024 at 11:53 PM William Miller via RE-wrenches
<re-wrenches at lists.re-wrenches.org> wrote:
>
> Friends:
>
>
>
> I found a grid-tie battery-backup system with a 120/240 VAC critical loads sub-panel that has no neutral run to it. All of the 120 VAC loads have their neutrals land in the meter panel.
>
>
>
> I have always felt instinctively that the neutrals should land in the breaker panel that feeds the circuit. I have looked through the NEC to find a passage that spells this out but I can seem to find one.
>
>
>
> Is this a code requirement? Is this recommended practice?
>
>
>
> Thanks in advance.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985