[RE-wrenches] Dual battery bank switch for 48 VDC system
greg egan
greg at remotepowerinc.com
Sat Jun 15 10:18:23 PDT 2024
Wrenches, I have a customer who has a 2 strings of AGM's @ 48 VDC that
we want to split so we can charge them at decent charge rate. Adding
more PV and/or larger generator and inverter is cost prohibitive. I've
seen Blue Seas (#3002) 4 position 500 amp switches that are rated for
32VDC. Max he could possibly pull at once with his system is less than
100 amps.
I would assume the Blue Seas 3002 would work and I'd probably use it in
my garage, but I'm not comfortable recommending it to a customer. Any
suggestions on a 60 VDC rated unit that could handle say 150 amps and
4/0 cables?
Maybe I'm being too cautious since the max load would be < 6KW and the
3002 is rated for 16kW load (32 VDC /500A)? Thoughts?
Thank you,
Greg Egan
Remote Power Inc.
Fairbanks, AK
More information about the RE-wrenches
mailing list