[RE-wrenches] XW Pro Firmware 2.04 melting devices
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Sat Apr 27 09:08:32 PDT 2024
Might want to get him to buy a voltmeter and safety glasses. Pretty
dangerous for anyone to do an EQ without a second set of eyes😉
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2024-04-26 5:26 pm, Eric Smiley via RE-wrenches wrote:
> I postpone firmware updates now.
>
> I had a Conext SW inverter that stopped equalizing after a firmware
> update . The client thought they were equalizing and the inverter said
> it was equalizing but the voltage never went above bulk during
> equalizing.
>
> I miss the dumb inverters.
>
> Eric Smiley (he/him) - Design Manager
> 250.703.6004
> eric at vecoop.ca
> 888.386.0116
> 3-4997 Polkey Rd, Duncan BC, V9L 6W3
> viridiansolar.ca [1]
>
> Viridian Solar honours the ancestral grounds on which we live and
> provide services, recognising that these lands are unceded Indigenous
> territory. We are steadfast in our commitment to reconciliation and
> acknowledge the rich history and traditions that characterise this land
> that we all consider home.
>
> On Fri, 26 Apr 2024 at 16:59, Kevin Pegg via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
>> Following up on the issue I reported earlier this week. Schneider has
>> finally admitted there are flaws in 2.04 firmware.
>>
>> "I'm sorry to hear about your issues with generator interaction with
>> the XWPro inverter. Investigation of this issue has found that certain
>> generators will exhibit unstable ac output under certain conditions of
>> charger power and load level. We are confident that we can roll out a
>> firmware fix to address this issue in the coming weeks (or sooner).
>> Meanwhile we recommend using firmware version 1.11 on sites which use
>> generators. "
>>
>> I downgraded the firmware today for a client who lives nearby and was
>> experiencing extreme power quality issues while generator running.
>> Testing the power quality before and after confirms that firmware 1.11
>> does resolve the issue.
>>
>> I may well leave off-grid clients reliant on backup generators on 1.11
>> unless there is a compelling reason for the newest. The one feature I
>> have been requesting for a couple years now is to re-enable generator
>> charging on AC1, which the XWPro currently does not support. We have
>> many off-grid clients with dual generators on XW6048's who lost that
>> functionality when upgrading to XWPros.
>>
>> Kevin
>>
>> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On
>> Behalf Of Kevin Pegg via RE-wrenches
>> Sent: April-25-24 10:25 AM
>> To: re-wrenches at lists.re-wrenches.org
>> Cc: Kevin Pegg <kpegg at energyalternatives.ca>
>> Subject: [RE-wrenches] XW Pro Firmware 2.04 melting devices
>>
>> Hi Wrenches,
>>
>> Curious if anyone else has seen this issue.
>>
>> New XW Pro off-grid system installed Dec 2023. Pretty standard config
>> for us, XW Pro, 5 kW PV, 50 kWh UnigyII battery, 8 kW high quality
>> diesel generator. This system ran fine all winter long - powering
>> customer's big RV they were living in while the house is built, Shop,
>> computer controlled outdoor wood boiler, domestic loads + 3 person
>> construction crew. Gen ran daily on auto start as we don't get much
>> sun Dec - Feb. No issues reported.
>>
>> Couple weeks back I did a new system check up. All performing well,
>> happy client. Part of that service I upgraded the XW firmware from
>> 1.09 to 2.04, and insight from 1.16 to 1.18. Gave the system a quick
>> check, ran gen. Lots of sun now, batteries full so didn't do a long
>> generator test. Yes I set the region codes for off-grid.
>>
>> A week later, while I was out of town and it was not so sunny so gen
>> running, client and their electrician called me in a panic. Two smoke
>> detectors had literally melted, as well as several dimmable LED
>> fixtures all failed. Electrician replaced the burned up devices, only
>> to have the same thing repeat a few days later. Talking with them it
>> was only when the generator was running there were issues. Told them
>> to lock out gen and I will get there when I can.
>>
>> Once back I attended site, fired up gen, and could hear the inverter
>> sounding terrible during gen charging. Lights flickering bad, and I
>> personally verified the smoke detectors beeping and getting warm and
>> the house smelled like burned plastic. I hooked up my power quality
>> analyser and could see the THD gradually building to over 36%. Gen
>> voltage was at 125/250V a bit high, so adjusted that, but no change.
>> By reducing the charge rate on the XW Pro to 50% was able to get the
>> THD down around 12% and less light flicker. But it's still too high.
>> Image attached shows THD with gen on original programing, then at
>> reduced charge rate.
>>
>> Have now gone from a happy client to a pissed off client threatening
>> legal action for endangering their lives & a bill from the
>> electrician. Ugh. Having a hard time explaining this to the client why
>> a system previously working fine went sideways so badly. Old guy
>> blames the "darned computer stuff" and he's not wrong with that
>> opinion.
>>
>> At another site, similar config but larger system with dual XW's that
>> I upgraded to 2.04 firmware remotely few days ago and now the two
>> inverters are literally fighting each other under generator charge -
>> one load building to +6 kW and one (minus)6 kW.
>>
>> Sure makes me reluctant to upgrade firmware on systems that are
>> working fine.
>>
>> Any suggestions?
>>
>> Kevin
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
Links:
------
[1]
https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-html&ust=1702155901939000&usg=AOvVaw3SHpXB-WRSlzWmjpz4htqG
[2] http://members.sti.net/offgridsolar/
[3] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240427/1bb96848/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 724429 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240427/1bb96848/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240427/1bb96848/attachment-0001.gif>
More information about the RE-wrenches
mailing list