[RE-wrenches] XW Pro Firmware 2.04 melting devices

Eric Smiley eric at vecoop.ca
Fri Apr 26 17:26:30 PDT 2024


I postpone firmware updates now.

I had a Conext SW inverter that stopped equalizing after a firmware update
. The client thought they were equalizing and the inverter said it was
equalizing but the voltage never went above bulk during equalizing.

I miss the dumb inverters.

Eric Smiley (he/him) - Design Manager

 250.703.6004
 eric at vecoop.ca
 888.386.0116
 3-4997 Polkey Rd, Duncan BC, V9L 6W3
 viridiansolar.ca
<https://www.google.com/url?q=https://viridiansolar.ca&source=gmail-html&ust=1702155901939000&usg=AOvVaw3SHpXB-WRSlzWmjpz4htqG>



Viridian Solar honours the ancestral grounds on which we live and provide
services, recognising that these lands are unceded Indigenous territory. We
are steadfast in our commitment to reconciliation and acknowledge the rich
history and traditions that characterise this land that we all consider
home.



On Fri, 26 Apr 2024 at 16:59, Kevin Pegg via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Following up on the issue I reported earlier this week. Schneider has
> finally admitted there are flaws in 2.04 firmware.
>
>
>
> “I’m sorry to hear about your issues with generator interaction with the
> XWPro inverter. Investigation of this issue has found that certain
> generators will exhibit unstable ac output under certain conditions of
> charger power and load level. We are confident that we can roll out a
> firmware fix to address this issue in the coming weeks (or sooner).
> Meanwhile we recommend using firmware version 1.11 on sites which use
> generators. “
>
>
>
> I downgraded the firmware today for a client who lives nearby and was
> experiencing extreme power quality issues while generator running. Testing
> the power quality before and after confirms that firmware 1.11 does resolve
> the issue.
>
>
>
> I may well leave off-grid clients reliant on backup generators on 1.11
> unless there is a compelling reason for the newest. The one feature I have
> been requesting for a couple years now is to re-enable generator charging
> on AC1, which the XWPro currently does not support. We have many off-grid
> clients with dual generators on XW6048’s who lost that functionality when
> upgrading to XWPros.
>
>
>
> Kevin
>
>
>
>
>
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
> Behalf Of *Kevin Pegg via RE-wrenches
> *Sent:* April-25-24 10:25 AM
> *To:* re-wrenches at lists.re-wrenches.org
> *Cc:* Kevin Pegg <kpegg at energyalternatives.ca>
> *Subject:* [RE-wrenches] XW Pro Firmware 2.04 melting devices
>
>
>
> Hi Wrenches,
>
>
>
> Curious if anyone else has seen this issue.
>
>
>
> New XW Pro off-grid system installed Dec 2023. Pretty standard config for
> us, XW Pro, 5 kW PV, 50 kWh UnigyII battery, 8 kW high quality diesel
> generator. This system ran fine all winter long – powering customer’s big
> RV they were living in while the house is built, Shop, computer controlled
> outdoor wood boiler, domestic loads + 3 person construction crew. Gen ran
> daily on auto start as we don’t get much sun Dec – Feb. No issues reported.
>
>
>
> Couple weeks back I did a new system check up. All performing well, happy
> client. Part of that service I upgraded the XW firmware from 1.09 to 2.04,
> and insight from 1.16 to 1.18. Gave the system a quick check, ran gen. Lots
> of sun now, batteries full so didn’t do a long generator test. Yes I set
> the region codes for off-grid.
>
>
>
> A week later, while I was out of town and it was not so sunny so gen
> running, client and their electrician called me in a panic. Two smoke
> detectors had literally melted, as well as several dimmable LED fixtures
> all failed. Electrician replaced the burned up devices, only to have the
> same thing repeat a few days later. Talking with them it was only when the
> generator was running there were issues. Told them to lock out gen and I
> will get there when I can.
>
>
>
> Once back I attended site, fired up gen, and could hear the inverter
> sounding terrible during gen charging. Lights flickering bad, and I
> personally verified the smoke detectors beeping and getting warm and the
> house smelled like burned plastic. I hooked up my power quality analyser
> and could see the THD gradually building to over 36%. Gen voltage was at
> 125/250V a bit high, so adjusted that, but no change. By reducing the
> charge rate on the XW Pro to 50% was able to get the THD down around 12%
> and less light flicker. But it’s still too high. Image attached shows THD
> with gen on original programing, then at reduced charge rate.
>
>
>
> Have now gone from a happy client to a pissed off client threatening legal
> action for endangering their lives & a bill from the electrician. Ugh.
> Having a hard time explaining this to the client why a system previously
> working fine went sideways so badly. Old guy blames the “darned computer
> stuff” and he’s not wrong with that opinion.
>
>
>
> At another site, similar config but larger system with dual XW’s that I
> upgraded to 2.04 firmware remotely few days ago and now the two inverters
> are literally fighting each other under generator charge – one load
> building to +6 kW and one (minus)6 kW.
>
>
>
> Sure makes me reluctant to upgrade firmware on systems that are working
> fine.
>
>
>
> Any suggestions?
>
>
>
> Kevin
>
>
>
>
>
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240426/c8535232/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 724429 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240426/c8535232/attachment-0001.jpg>


More information about the RE-wrenches mailing list