[RE-wrenches] PV/Charge Controller Troubleshoot Help

toddcory at finestplanet.com toddcory at finestplanet.com
Tue Apr 23 11:47:31 PDT 2024


My old MX60 said " hot" when the fan had failed.Todd

"MX 2 Hot (Very rare) Either the MX60 is too hot or its internal temperature sensor is shorted. If this message appears, carefully check if the MX60’s heat sink is extremely hot. The heat generated by the MX60, and therefore its losses, is proportional to input voltage times output current. Avoid installing the MX60 in direct sunlight to help control its operating temperature."
 


On Tuesday, April 23, 2024 11:19am, "William Miller via RE-wrenches" <re-wrenches at lists.re-wrenches.org> said:



> If the fan fails would there be an error message? As always, I looked this
> up before posting. The manual is not clear on the matter.
> 
> William
> 
> Miller Solar
> 17395 Oak Road, Atascadero, CA 93422
> 805-438-5600
> www.millersolar.com
> CA Lic. 773985
> 
> 
> -----Original Message-----
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of MDElectricSolar via RE-wrenches
> Sent: Tuesday, April 23, 2024 6:58 AM
> To: RE-wrenches
> Cc: MDElectricSolar
> Subject: Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help
> 
> It may be the fan. I had an FM 80 where the fan went bad that caused very
> limited solar production throughout the day.
> 
> Michael D Nelson
> MD Electric & Solar, Inc.
> 707-684-0064 mobile
> 707-884-1862 office
> www.mdelectricsolar.com
> www.facebook.com/mdelectricandsolar
> 
> 
> > On Apr 23, 2024, at 6:54 AM, jay via RE-wrenches
> > <re-wrenches at lists.re-wrenches.org> wrote:
> >
> > HI Jim,
> >
> > The CC is sure suspect.
> > You didn’t mention what the battery voltage is.
> > Those CC have a hard PV watt input limit.
> >
> > You can try and set it back to factory default and then reprogram,
> > sometimes that works.
> >
> > I don’t use the FM-60, but always the FM-80 because of the fan
> > replacement. the 80 takes 3 minutes, the 60 takes 2 hours.
> >
> > jay
> >
> >> On Apr 23, 2024, at 6:00 AM, Jim Gowdy via RE-wrenches
> >> <re-wrenches at lists.re-wrenches.org> wrote:
> >>
> >> I'm troubleshooting the solar aspect of a small offgrid 120v outback
> >> system and need some opinions. The customer was complaining that the
> >> generator was running too much so I went out to their property and
> >> investigated. The solar array consists of 16 total panels (4 strings of
> >> 4). At the combiner box, I took the voltage and amperage reading of each
> >> string and found the following......BREAKER 1 (85VDC/8.87A) BREAKER 2
> >> (84.5VDC/8.9A) BREAKER 3 (.03VDC/0A) BREAKER 4(85VDC/8.89A). Breaker 3
> >> string was not producing and so I did a fix and then read
> >> (87.1VDC/8.43A). After reviewing the online monitor since that fix from
> >> a few days prior I'm realizing that the first day after had 4.5KWH
> >> production, second day had 0.7KWH production, and yesterday had 0.3KWH
> >> production.....sun has been out without clouds. The 60A Outback charge
> >> controller shows there is PV voltage, but noticed it was in "silent mode"
> >> a good amount of time. Charge controller is old, but all the other
> >> equipment was updated about a year and a half ago. I was wondering if
> >> there is a way to diagnose if the charge controller is bad without just
> >> replacing it and what does it mean when it's in "silent mode". Another
> >> side note is that their generator threw an AGS fault code on the MATE3
> >> controller and found that the generator has problems so I ended up
> >> turning from "auto" to "off"
> >> --
> >> Jim with Gowdy Electric
> >> Cambria, Ca 93428
> >> business 805 927 2630
> >> cell 805 975 5279
> >> _______________________________________________
> >> List sponsored by Redwood Alliance
> >>
> >> Pay optional member dues here: http://re-wrenches.org
> >>
> >> List Address: RE-wrenches at lists.re-wrenches.org
> >>
> >> Change listserver email address & settings:
> >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >>
> >> There are two list archives for searching. When one doesn't work, try the
> >> other:
> >> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >>
> >> List rules & etiquette:
> >> http://www.re-wrenches.org/etiquette.htm
> >>
> >> Check out or update participant bios:
> >> http://www.members.re-wrenches.org
> >>
> >
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > Pay optional member dues here: http://re-wrenches.org
> >
> > List Address: RE-wrenches at lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > There are two list archives for searching. When one doesn't work, try the
> > other:
> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > http://www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > http://www.members.re-wrenches.org
> >
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> 


Sent from Finest Planet WebMail.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240423/26953809/attachment.htm>


More information about the RE-wrenches mailing list