I second using the 48v to 12 v DC DC converter. I've had success with
that, and avoided the issues Jeremy mentioned.
Ray Walters
Remote Solar
On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote:
> I powered a MidNite LSOB transmitter from a Classic AUX, though the
> receivers didn't work with the Classic. The Classic is limited to
> 200ma output and the Tigo and APS transmitters are rated at up to
> 800ma input, so it might overload the Classic AUX output if they
> really do draw that much.
>
> I tested an APS RSD system recently with a Classic and it did not work
> well. I believe that the Tigo transmitter is very similar since the
> APS devices say "licensed by Tigo" on them, So, the Tigo RSD devices
> may not work well with a Classic either.
>
> What I recommended while at AEE was to use a 48VDC to 12VDC converter
> to power the Tigo and APS transmitters. This works well. Here's the
> one I recommended if it's still available: mean-well/ddr30l12
> <https://www.onlinecomponents.com/mean-well/ddr30l12-50161036.html>
> I never had any negative feedback using this with a Sol-Ark and APS
> devices.
>
> With a Classic in the system I've had to use the FireRaptor RSD
> devices. If you can get approval or have older modules, you might be
> able to follow the FireRaptor instructions and use 2 modules in series
> for each FireRaptor. You do still have to have a way to disconnect the
> PV output circuit from the Classic in order to make that circuit dead
> from the Classic end of the circuit. I did that by putting an
> MNPV6-disco on the power shed which disconnects the PV output circuit
> as well as the 24VDC to the FireRaptors. And, I am powering my
> FireRaptors at 15VDC and it works fine.
>
> Brad Bassett, ret.
>
>
>
>
> On Fri, Feb 16, 2024 at 6:47 PM Jeremy Rodriguez via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Has anyone successfully used a MidNite Classic CC to power a Tigo
> Rapid Shutdown Transmitter in an off grid setting ? Specifically
> using the 12v Aux output to keep the PV circuits alive instead of
> relying on the inverter AC output to do this.
>
> Think of this scenario. Batteries reach LBCO, inverter shuts OFF,
> no PV to re charge back to LBCI, no generator backup to recharge
> batteries.
>
>
> Jeremy Rodriguez
> Solar Installation / Design
> All Solar, Inc.
> 1453 M St.
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work,
> try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240217/ed6ba243/attachment.htm>
More information about the RE-wrenches
mailing list