What is the array size vs the battery size?  Sounds like a big array on 
a small battery for the voltage to go that high that fast.

Ray
Remote Solar

On 10/21/2023 5:46 PM, William Miller via RE-wrenches wrote:
> Friends:
>
> I’m kinda stuck on a project setting up a SI/SB AC coupled system off 
> grid. When the SB inverters ramp up the battery voltage jumps to 69 
> pretty quickly and the system shuts off.
>
> I checked the mini-grid frequency and it does ramp up to about 62+ but 
> apparently not soon enough to curtail charging. I shut off the SBs for 
> now and we can rely on generator.
>
> Any advice via email or a phone call would be appreciated.  SMA can be 
> less than helpful, especially for systems with lithium batteries.
>
> Thanks in advance.
>
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com <http://www.millersolar.com>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20231021/5d19f8e5/attachment.htm>


More information about the RE-wrenches mailing list