[RE-wrenches] sol ark AGS question
Michael Morningstar
mjmorningstar at gmail.com
Fri Sep 15 05:26:36 PDT 2023
We learned of this major deficiency after an eight unit install. No cool
down is disastrous to modern diesels. Our work around was installing a
400amp contactor and macromatic programmable relay.
On Thu, Sep 14, 2023 at 10:05 PM Jerry Shafer via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Jay, wrenches
> ASCO makes multiple ATS controls that can manage delays latching up and
> for cool down. Most of the gensets have are programmed cool down after
> relay opens so its not an issue. Generally on start up the genny connects
> as soon as it's voltage and freq are within range.
> fun times
>
>
>
> On Thu, Sep 14, 2023, 2:26 PM jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Hi All,
>>
>> I have a client with a sol ark and it doesn’t have warm up or cool down,
>> kind of amazing companies are going backwards in their tech.
>>
>>
>> Has anyone come up with external fix for this?
>>
>> I am guessing the internal relay on the sol ark switches closed when it
>> sees the correct volts/hz and opens the sol ark relay when it sends the off
>> signal.
>>
>> If thats correct I can pretty easily use a delay relay on the off cycle
>> assuming the on signal has a time window to allow for this delay in sending
>> power to the inverter.
>>
>> The on delay I don’t see anyway unless I use a contactor with on delay
>> relay.
>>
>> Maybe there is a off the shelf generator transfer switch that has this
>> built in?
>>
>> Thanks in advance
>>
>> Jay
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Michael Morningstar
Morningstar Electric
PO Box 1494
Mount Shasta, CA 96067
530-921-0560
mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230915/a4c8fc07/attachment.htm>
More information about the RE-wrenches
mailing list