[RE-wrenches] Outback lithium LVD
Jerry Shafer
jerrysgarage01 at gmail.com
Thu Jul 20 21:38:11 PDT 2023
Jay
I don't seem to have an issue set the inverter to shut down befor the
battery and the CCwill begin to charge again untill voltage rises enough to
start the inverter back up. Also set the genny to come on even above the
inverter voltage so a shut down does not even accure. If you use lithium
don't connect the battery temp sensor, it will mess up the chargers.
Fun times
On Thu, Jul 20, 2023, 4:11 PM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I apologize in advance if this is a duplicate.
>
> I was contemplating the discussion about how to deal with an inverter that
> doesnt have the correct LBCO for a lithium LVD voltage.
>
> A suggested option for OB was to install a relay triggered by the AUX and
> controlling the inverter remote on/off switch.
>
> But if the aux switches, then the inverter is off and you won’t be able to
> charge with a generator. Right?
>
> I’m asking as I have this exact situation and I’m planning on a relay on
> the ac inverter output so the client can just turn on the generator and
> it’ll charge up.
>
> Am I missing something?
>
> Thanks
> Jay
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230720/29d7c133/attachment.htm>
More information about the RE-wrenches
mailing list