[RE-wrenches] High current dc combiner vibration

Jerry Shafer jerrysgarage01 at gmail.com
Thu Jun 29 21:39:39 PDT 2023


Kirk
As the batteries come up to charge does the vibration subside. Are the
battery cables spun together "corkscrew like" l have seen this correct DC
noise. I have an 8 on 8 just like your 10 and l have no noise at all, mine
come in from each side of the battery combiner, how is your install
configured, how is the cable length same close or very short to very long
some length is better on FLA's due to resistance under load and charge.
More information may help with a solution.
Fun times solar
NABCEP PV Inspector

On Thu, Jun 29, 2023, 8:19 AM Kirk Herander via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> All,
>
> I am in the middle of commissioning a 480kwh BP LFP battery bank,
> connected to -10- OB Radian 8kw inverter/chargers.
>
> For the DC combiner I am using midnite 2000 amp combiner boxes, modified
> to mount  class T fuses on the positive bus, for both battery inputs and
> inverter outputs.
>
> For starters, I set the master inverter at a max charge rate of 20 AC
> amps, which equates to a DC charge of about 74 A. All the other inverters
> are automatically set to this charge rate as well.
>
> Turning the chargers on one by one, I started to get quite an audible
> vibration from the combiner box at a combined charge of about 400 to 500 A.
>
> So I took the cover off of the combiner, which was vibrating noticabllly
> by feel. Most of the noise was from the cover not fitting tight. But the
> The box itself is also vibrating by feel.
>
> I took the combined charge up to 640A dc. This level of vibration
> definitely increases with an increased charge rate. And I am surprised
> because after all, we’re not talking AC here we’re talking DC. It almost
> reminds me of a large AC transformer in its behavior. The vibration did not
> seem to be originating at the inverters, then resonating to the combiner.
>
> I can dampen the vibration by adding a few things, but I’m surprised that
> this is happening. All connections in the combiner are tightened properly.
> Ideas?
>
>
>
>
>
>
>
>
>
>
> --
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 32st Anniversary 1991-2023!!*
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230629/bf918906/attachment.htm>


More information about the RE-wrenches mailing list