[RE-wrenches] 1000Vdc Combiner Block, Fusing

Kirk Herander kirkh at vermont.solar
Wed Mar 1 10:39:54 PST 2023


Yes there is a definite need for 1000vdc Combiner. it does not exist
without as you say custom work by BOS or others.

This was mentioned in past threads but I ended up building my own for a 1
mwh high voltage LFP system. All ul Components and fusing, but inspection
was not required.

Contact me off list no give you a de facto BOM of Items used.

On Wed, Mar 1, 2023 at 9:44 AM Mac Lewis via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> Thanks Daniel, yes I was hopeful with SolarBOS, but they let me know they
> are unable to do this right now.  I may need to do a fully custom solution
> but that's always iffy with inspectors.  This really should be a product at
> this point so I'm a bit surprised how difficult it is to find something.
>
> Thanks!
>
> On Wed, Mar 1, 2023 at 7:32 AM Daniel Young <danny at sesre.com> wrote:
>
>> Have not used them in some time, but used to a LOT and generally happy
>> with them.
>>
>>
>>
>> http://www.solarbos.com/Products
>>
>>
>>
>> Lead times were a bit long, in the 1-2 month range, but who knows what
>> they are now, last time I used them was pre-pandemic.
>>
>>
>>
>> --
>>
>>
>>
>> Danny Young
>>
>> NABCEP PV Installation Professional #031508-90
>>
>> Engineering Team Lead
>> Solar Energy Solutions
>>
>> Lexington | Louisville | Bloomington | Cincinnati | Evansville |
>> Indianapolis
>>
>> 513-448-5176 (mobile)
>>
>> 877-312-7456 (Main Office)
>>
>> danny at sesre.com
>>
>>
>>
>> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On
>> Behalf Of *Mac Lewis via RE-wrenches
>> *Sent:* Sunday, February 26, 2023 10:54 AM
>> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> *Cc:* Mac Lewis <maclewis1 at gmail.com>
>> *Subject:* [RE-wrenches] 1000Vdc Combiner Block, Fusing
>>
>>
>>
>> Good Morning Wrenches,
>>
>>
>>
>> I am looking for suggestions on suppliers that work in the 1000Vdc UL
>> listed equipment space.  Specifically, I'm trying to build a 1000Vdc rated
>> combiner (Combining 4 x 100A rated battery outputs up to 900Vdc) as well as
>> add OCPD (fuse or breaker) on the output going to the storage inverter.
>> I'd love to find a packaged UL listed combiner for this, but I've had no
>> luck with that.  Any suggestions/supplier contacts are appreciated
>>
>>
>>
>> Thanks!
>>
>>
>>
>> --
>>
>>
>>
>>
>>
>>
>>
>> Mac Lewis
>>
>> "Yo solo sé que no sé nada." *-Sócrates*
>>
>
>
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --

*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 32st Anniversary 1991-2023!!*

dba Vermont Solar Engineering

802.863.1202
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230301/8d625cb4/attachment.htm>


More information about the RE-wrenches mailing list