[RE-wrenches] Low Frequency transformer off-grid inverter options

Starlight larry at starlightsolar.com
Fri Jan 13 10:54:08 PST 2023


Any new AC equipment connected and running during test? Scope the waveform during equipment start to see if the distortion is severe. I have seen a 300W load make a mess of a Magnum AC waveform.

Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:48 AM, Mac Lewis <maclewis1 at gmail.com> wrote:

Good question Larry, 

Rock solid 52V on a lithium battery system. Doesn't appear to be a battery problem at all. 

On Fri, Jan 13, 2023, 11:41 AM Starlight <larry at starlightsolar.com <mailto:larry at starlightsolar.com>> wrote:
Mac,

What was the lowest voltage measured at inverter battery terminals during the inrush measurement?

Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:

Hello Wrenches,

I have a new client that has ran a pretty decent wood shop for about 10 years on a Magnum 4448.  He's got some large loads, planers, saws, compressors vacuums etc.  They are really nice, heavy duty pieces of equipment.  Amazingly, the Magnum has been able to start these loads for the most part for 10 years, but he has reported that it has gotten worse lately (could be a load issue), brown outs, dimming etc

He wants to upgrade the system, get remote monitoring etc.  I tried a test with a Sol-Ark 12, and it won't start these large motor loads.  I was a little surprised by that but I know they aren't as good as the low freq transformer based inverters at these surges.

I confirmed that its not just an overload from imbalance because the 240V loads will also overload it.  I got an inrush measurement of 48.5A Ac @240 (but it didn't start the load before Sol-Ark would shut off)  

What are my options?
Schneider XW Pro 6848
Outback Radian 8048 (Is this a low freq device?)
Sunny Islands are beasts but weird to work with and not user friendly

Any others I should consider?  He does have some significant 120 only loads so I don't think the Outback vfxr are a good choice.

Is it as simple as saying if the Magnum can start this load, the Radian should?

I appreciate your input!

--