[RE-wrenches] Low Frequency transformer off-grid inverter options
Mac Lewis
maclewis1 at gmail.com
Fri Jan 13 10:48:01 PST 2023
Good question Larry,
Rock solid 52V on a lithium battery system. Doesn't appear to be a battery
problem at all.
On Fri, Jan 13, 2023, 11:41 AM Starlight <larry at starlightsolar.com> wrote:
> Mac,
>
> What was the lowest voltage measured at inverter battery terminals during
> the inrush measurement?
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
>
> On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> Hello Wrenches,
>
> I have a new client that has ran a pretty decent wood shop for about 10
> years on a Magnum 4448. He's got some large loads, planers, saws,
> compressors vacuums etc. They are really nice, heavy duty pieces of
> equipment. Amazingly, the Magnum has been able to start these loads for
> the most part for 10 years, but he has reported that it has gotten worse
> lately (could be a load issue), brown outs, dimming etc
>
> He wants to upgrade the system, get remote monitoring etc. I tried a test
> with a Sol-Ark 12, and it won't start these large motor loads. I was a
> little surprised by that but I know they aren't as good as the low freq
> transformer based inverters at these surges.
>
> I confirmed that its not just an overload from imbalance because the 240V
> loads will also overload it. I got an inrush measurement of 48.5A Ac @240
> (but it didn't start the load before Sol-Ark would shut off)
>
> What are my options?
> Schneider XW Pro 6848
> Outback Radian 8048 (Is this a low freq device?)
> Sunny Islands are beasts but weird to work with and not user friendly
>
> Any others I should consider? He does have some significant 120 only
> loads so I don't think the Outback vfxr are a good choice.
>
> Is it as simple as saying if the Magnum can start this load, the Radian
> should?
>
> I appreciate your input!
>
> --
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230113/bb601eb8/attachment.htm>
More information about the RE-wrenches
mailing list