[RE-wrenches] Radian / Flexmax issue

drake.chamberlin at redwoodalliance.org drake.chamberlin at redwoodalliance.org
Thu Nov 10 05:21:10 PST 2022


Suzanne finally did get the system working. The problem was in the 
programming of the Mate. This was discovered by Outback Tech support 
with Optics. So far, no word on the exact settings involved. The 
batteries were not damaged.

Thank you for your help.

Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor's License 44810
CO Master Electrician's License 4526
NABCEP Certified PV Installation Professional


---


On 2022-10-28 07:53, Tump via RE-wrenches wrote:

> ISOLATE ISOLATE ISOLATE. The first thing I would do id disable the Flex 
> net DC, next isolate each 12 v battery, ck voltages, load test,  use  
> any automotive battery tester find 4 decent batteries and try again. 
> Have you replaced all the com cables? Cheap and w/ the possibility of 
> Lightning strike, its a no brainer. I have seen the FNDC cause all 
> sorts of issues due to battery issues. We at one time installed quite a 
> few only to have issues w/ batteries that were undercharged, customers 
> restarting the system w/ batteries that were not fully charged. When 
> rebooted the FNDC is assuming that the batteries ARE FULLY CHARGED and 
> have the rated capacity, which usually NOT the case.
> Firmwares versions are easily found in the "system info" in the M3s
> 
>> On Oct 26, 2022, at 8:04 PM, Drake Chamberlin via RE-wrenches 
>> <re-wrenches at lists.re-wrenches.org> wrote:
>> 
>> Hello All,
>> 
>> Suzanne Csejtey of Design Energy contacted me with an Outback Radian / 
>> Flexmax 80 system problem. I don't know what is going on with this 
>> system. Below is her description of the problem. Any help would be 
>> appreciated.
>> --------------------------------------------------------------------------
>> System installed 2014.
>> 
>> 6.6kW PV, Outback Radian 8048 inverter, (2) x Midnite Classic 200 
>> charge controllers, 600Ah
>> Battery bank (12 x 12V 200Ah Outback Energycell ) for backup of 100A 
>> aux panel
>> 
>> It worked great, but the customer was always disappointed that she 
>> couldn't show her system
>> online on one screen, because the Midnite charge controllers didn't 
>> talk to the Outback Mate 3.
>> In 2017 the charge controllers were changed to (2) x Outback Flexmax 
>> 80's, and problems
>> started a couple years after that. The system would shut down at least 
>> once a month, start up
>> the next day, and the electrician couldn't find the problem but 
>> suspected grid instability. Outback tech support couldn't help until 
>> the system was on OpticsRE, late 2021. Tech support resolved the 
>> shutdown issue this year with 2 nd firmware upgrade and a few settings 
>> adjusted on Mate3.
>> 
>> Radian GS8048 updated 2021, verified 8/2022 from tech support but I am 
>> not finding the
>> firmware number. August 2022 tech support walked through our settings 
>> and verified all ok with batteries, CCs. Adjusted Mate3 to establish 
>> OpticsRE connection, verified not selling from
>> battery/backup only.
>> 
>> Worked very well until this September when a lightning storm 
>> apparently took out the internet
>> modem and inverter comms with it. Solar and battery still working. 
>> Outback told us to replace
>> the Mate3 and Hub, and then the FlexNet DC monitor. Latest firmware 
>> update attempted on
>> new Mate3s when received, 001.004.007 but it was already installed and 
>> ready to go.
>> 
>> Instead of setting everything up again from scratch after replacing 
>> Mate3 with Mate3S we
>> decided to see if the charge controllers would repopulate the old 
>> information, as recommended
>> in the Outback forum. Then tried to get help to verify settings from 
>> Outback support. Support
>> had been very helpful in the past but this time we weren't so lucky 
>> and the person just let us
>> know that wasn't their job and sent a link to the manual. But the 
>> batteries appeared to be at
>> 100%, set not to sell, backup only, max PV self-consumption. The plan 
>> was to find more help to
>> verify settings and keep an eye on the system.
>> 
>> Seemed to be working very well until it went
>> crazy last week, when the Mate showed alarm, batteries discharged down 
>> to 6%, then up to
>> 100%, then everything shut down completely.
>> 
>> Programming may be a big part of the issue. Also hearing that the age 
>> of the AGM batteries may have been a factor, 8 years. That sometimes 
>> dying batteries cause odd behavior?
>> ----------------------------------------------------------------
>> Thanks in advance.
>> 
>> Drake
>> 
>> Drake Chamberlin
>> Athens Electric LLC
>> Ohio Electrical Contractor's License 44810
>> CO Master Electrician's License 4526
>> NABCEP Certified PV Installation Professional
>> 
>> --
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try 
>> the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
> 
>> Tump3391 at gmail.com       www.SWNL.net
>> 
>> Solarwinds Northernlights   _    _
>> _       Serving Mid Coast Maine & Northern California_
>> _                         207-832-7574   Cl. 610-517-8401              
>>                 _
>> _                              __Blair "TUMP" May_
>> 
>> ********  MAINE'S CHARTER ********
>> _                   __  NABCEP    "Certified PV Installer"_
>> 
>> ********  MAINE'S CHARTER ********
>> _        Trace Xantrex "Certified" Dealer / Installer"_
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org


More information about the RE-wrenches mailing list