Hi Dave, 

Right. Attached is a Magnum AC coupled line diagram and also an
instruction sheet. On the line diagram, they show a diversion load, but
you will likely use a protective relay, set to trigger when voltage goes
over absorption for the batteries.  

Since Magnum doesn't have a voltage sensitive relay, you will probably
want to use a Morningstar Relay Driver (manual attached) to control the
protective relay. 

Best, 

Drake 

Drake Chamberlin 

Athens Electric LLC 

Ohio Electrical Contractor's License 44810 

CO Master Electrician's License 4526 

NABCEP Certified PV Installation Professional

---

On 2022-10-07 16:23, Dave Tedeyan via RE-wrenches wrote:

> Hi Drake,  
> Just to make sure I understand you correctly, I could tie in a new grid tie inverter on the load side of the Magnum inverter. Then when the grid is up, the power will be able to backfeed through the MMP175-30D panel to the AC input (which will get rewired to the grid). And when the grid is down, the Magnum inverter will be able to take the power from the grid tie inverter on the load side of the Magnum inverter to charge the batteries? 
> Cheers, 
> Dave 
> 
> On Fri, Oct 7, 2022 at 1:00 PM Drake Chamberlin via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote: 
> 
> The grid tie inverter can sell through the Magnum relay. When the grid goes down, it will feed the batteries. 
> 
> Drake Chamberlin 
> 
> Athens Electric LLC 
> 
> Ohio Electrical Contractor's License 44810 
> 
> CO Master Electrician's License 4526 
> 
> NABCEP Certified PV Installation Professional
> 
> ---
> 
> On 2022-10-07 11:42, Dave Tedeyan via RE-wrenches wrote: 
> 
> Hi All,  
> 
> I've got someone who wants to tie their off-grid system with a Magnum inverter (which I think is a 4024 PAE inverter) to the grid. Since the Magnum inverter cannot be grid tied, I was wondering if there is some kind of simple grid tie inverter that can be the grid interface, while keeping the existing system in tact.  
> 
> Otherwise, I see two paths here. The less expensive path would be to ditch the batteries and connect the panels to a grid tie inverter. Otherwise it seems that we will need to get another battery based inverter that is meant to be grid connected to replace the Magnum. 
> 
> Cheers, 
> Dave
> -- 
> 
> [1]
> 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> 
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com [2]
> c: (607) 288-2898 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

  -- 

 		 [1]

 Dave Tedeyan, P.E.
Owner | Sungineer Solar

 p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com [2]
c: (607) 288-2898 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

 

Links:
------
[1] https://www.sungineersolar.com/
[2] http://www.sungineersolar.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221008/7cfb89b7/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Magnum AC Coupled Line Diagram (1-May-2010).pdf
Type: application/pdf
Size: 257350 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221008/7cfb89b7/attachment-0003.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: AN 0002 AC Coupling (Rev 5-10).pdf
Type: application/pdf
Size: 158919 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221008/7cfb89b7/attachment-0004.pdf>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Relay Driver Manual.01.EN.pdf
Type: application/pdf
Size: 942281 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221008/7cfb89b7/attachment-0005.pdf>


More information about the RE-wrenches mailing list